I’ve got a two year old alpha boiler, with 13 radiators running off it.

Ever since it was fitted there has been pressure issues, the more it’s on - the less problems.
But when the weather gets better and the boiler is used less the pressure is dripping every night to zero.

I’ve checked all the visible pipe work and cannot find any issues all the radiators seem to be bled correctly.

Also, I switched the flow and return valves off overnight after I’d set the pressure at 2.5bar, it lost no pressure but as soon as I opened the valves the pressure dropped down to one very quickly.

It’s driving me up the wall, gas engineers I speak to arnt interested in helping me coz it’s a crap awkward job.

I’m wandering could it be that I need an external expansion vessel because I’ve got so many radiators

It’s a large Victorian semi
Could this be my problem

Any help and advice would be very grateful

Cheers

Michael
 
You’ve tested the boiler and it held up pressure so it’s a system issue any pipework in concrete floors ?
 
No
No solid floors
Only about 15ft of pipe work I can’t get to

I would if you could valve that part off and test overnight to see if it holds
 
Just to be clear, you mean that the pressure indicated on a gauge is falling overnight not that the pressure relief valve outlet is dripping?
 
Just to be clear, you mean that the pressure indicated on a gauge is falling overnight not that the pressure relief valve outlet is dripping?
The pressure on the boiler remained at 2.5bar
Overnight when the flow and return valves were closed

as soon as I opened them the following morning
It dropped like a brick to 1.0bar
 
The pressure on the boiler remained at 2.5bar
Overnight when the flow and return valves were closed

as soon as I opened them the following morning
It dropped like a brick to 1.0bar
Was the radiator system hot when everything was at 2.5 bar and you isolated the boiler? If so, there will be a rapid drop the following morning when you reconnect the boiler to the cold system.

Are you saying that you are having to keep adding water continually to the system to keep it running, i.e. there must be a leak from the radiator circuit and/or hot water cylinder?

You can test to see whether you need a larger expansion vessel by draining some water out of a radiator while leaving it's bleed nipple open. The idea is to get it half full of water with air trapped in the top half.

I think your problem is more likely to be a leak somewhere. The first step, obviously, is to have a careful look at everything to see if there are signs of damp / water / corrosion. Do this carefully because the next steps are harder work and/or a bit pricey.
 
Last edited:
Was the radiator system hot when everything was at 2.5 bar and you isolated the boiler? If so, there will be a rapid drop the following morning when you reconnect the boiler to the cold system.

Are you saying that you are having to keep adding water continually to the system to keep it running, i.e. there must be a leak from the radiator circuit and/or hot water cylinder?

You can test to see whether you need a larger expansion vessel by draining some water out of a radiator while leaving it's bleed nipple open. The idea is to get it half full of water with air trapped in the top half.

I think your problem is more likely to be a leak somewhere. The first step, obviously, is to have a careful look at everything to see if there are signs of damp / water / corrosion. Do this carefully because the next steps are harder work and/or a bit pricey.
Hi
The boiler was cold when it was out to 2.5bar and then switched off.

every morning the pressure is zero

I keep looking for leaks and cannot find anything at all
No water marks
No drips
No wet carpets or wet plaster
 
dropping from high (2.5) to 1 is a big step but it might represent a very small volume of water. Once it has dropped from 2.5 to 1, if you leave it, does it drop again to zero?
 

Reply to Loss of pressure when boiler is off in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
0
Views
44
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
6
Views
135
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
297
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
198
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
347
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock