Hi everyone, I’m completely new here and just signed up.
My Termet boiler has been leaking for a while, and I’ve been procrastinating honestly to do anything about it as the weather has been warm.
Yesterday my wife turned the heating up to the max which I told her not to do, anyway water was everywhere of course.
After reading a lot and watching some videos, I’m sure ( but please correct me if I’m wrong) that I need to replace the pressure relief valve. Also I assumed the expansion tank might need replacing too but when I opened the top part, I can’t see one??
Any tips on what my next step should be?I’ll include some pics.
Thanks!
 

Attachments

  • 9C543019-7ACF-4F64-8EC2-98ED37CC8F91.jpeg
    9C543019-7ACF-4F64-8EC2-98ED37CC8F91.jpeg
    333.1 KB · Views: 10
  • 1427E8F3-AC53-4149-81A6-E43AAC5C47A0.jpeg
    1427E8F3-AC53-4149-81A6-E43AAC5C47A0.jpeg
    306.7 KB · Views: 11
  • FDF01EB6-B826-476E-86A4-07D079154790.jpeg
    FDF01EB6-B826-476E-86A4-07D079154790.jpeg
    354.5 KB · Views: 9
  • 5D22483B-18CC-42C1-B4F9-06280F877FA0.jpeg
    5D22483B-18CC-42C1-B4F9-06280F877FA0.jpeg
    395.3 KB · Views: 13
1. I note you are in Poland, so the rules on who can do what with a boiler may be different from the UK.
2. I'm not familiar with your make of boiler, but it looks like an open vented (regular) boiler which has been attached to a sealed system. If so, expect to find the expansion vessel somewhere else.
3. The expansion vessel outlet should be connected by a copper pipe to the outside of the property. In the UK the end of this pipe would be "turned back" against a wall, usually by an elbow and a 45 degree fitting.
4. It may not be UK rules, but I would strongly suggest you leave meddling with the boiler to a trained and certified person.
 
1. I note you are in Poland, so the rules on who can do what with a boiler may be different from the UK.
2. I'm not familiar with your make of boiler, but it looks like an open vented (regular) boiler which has been attached to a sealed system. If so, expect to find the expansion vessel somewhere else.
3. The expansion vessel outlet should be connected by a copper pipe to the outside of the property. In the UK the end of this pipe would be "turned back" against a wall, usually by an elbow and a 45 degree fitting.
4. It may not be UK rules, but I would strongly suggest you leave meddling with the boiler to a trained and certified person.
Okay thank you!
I’ve taken both of pieces of advice and put the casing back on.
I assumed replacing both parts I mentioned would be a case of turning off, draining and replacing, only dealing with water, not gas which I don’t want to touch.
I presume the expansion tank is in the basement or attic?
One more question this casing that I took off, does it need to be 100% airtight? I don’t think so, but now after putting it back on the thought just occurred to me.
 

Attachments

  • 9B9DB8D4-818F-477A-9FA9-EC17DB3D679D.jpeg
    9B9DB8D4-818F-477A-9FA9-EC17DB3D679D.jpeg
    301.7 KB · Views: 8
  • 12B6CEF1-716B-4123-93A6-502D09488B28.jpeg
    12B6CEF1-716B-4123-93A6-502D09488B28.jpeg
    253.2 KB · Views: 6

Reply to Leaking safety valve in the USA area at PlumbersForums.net

Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock