Hi,
Im in the process of extending my home and I'm considering installing a Kitchen Island with sink and I'm concerned about waste. My extension foundation block are in and built up to current floor level - I've yet to put in the hardcore/insulation and concrete slab. My island will be 2.5m from outside wall of the new extension, where a Back inlet gully will sit and flow into the existing 100mm soil - vented stack. Would it be normal practise to leave a channel in the proposed concrete slab and simply run the sink waste through this and into the back of the new gully? I'll be using Hep20 pipe in pipe for hot and cold supply. Any advice would be grateful.

Thanks
 
Old school mentality:

Run 110mm on grade and reduce the vertical to 50mm to pick up the sink.
I would never run 40mm or 50mm on grade through a slab under any circumstances, more so on a kitchen sink
 
Thanks to you both for the advice. So if I run 100mm through does that get incased in the concrete slab (of which is 150) or does it run through the hardcore do u know -sorry more of a builder question I guess. I would then have to do a direct connection to the existing near by underground 100mm pipe and omit the BIG. I picked up the attached photo from polypipe website and that's where I thought the 50mm pipe would have been an option.

IMG_1276.JPG
 
Old school mentality:

Run 110mm on grade and reduce the vertical to 50mm to pick up the sink.
I would never run 40mm or 50mm on grade through a slab under any circumstances, more so on a kitchen sink

Totally agree, the extra £20 in materials is nothing compared to having to dig up your floor because you scrimped the first time.
 
Yep I agree. But i dont know where the 110mm pip should sit in the floor. I dont want to put my concrete in now until I know where it should sit. The building regs doc seems unclear.
 
I would avoid at all costs running drainage pipes in the slab.
Run it below the slab and connect to where you have to.

By the way, run your hot and cold piping from an accessible point, in a separate 110 mm pipe to the kitchen island.
That way, if there's a problem, you have 1/2 a chance of replacing it with minimal damage
 
Part H seems clear to me on requirements & also check out Diagram 11 & 12

2.23 A drain may run under a building if at least 100mm of granular or other flexible filling is provided round the pipe. On sites where excessive subsidence is possible additional flexible joints may be advisable or other solutions such as suspended drainage, particularly where the pipe is adjacent to structures or where soil conditions change in the course of the pipe run.
Where the crown of the pipe is within 300mm of the underside of the slab, special protection should be provided (see paragraph 2.44).

2.24 At any points where pipes are built into a structure, including an inspection chamber, manhole, footing, ground beam or wall, suitable measures should be taken to prevent damage or misalignment. This may be achieved by either:

a. building in a length of pipe (as short as possible) with its joints as close as possible to the wall faces (within at most 150mm) and connected on each side of rocker pipes by a length of at most 600mm and flexible joints (see Diagram 7(a)); or

b. forming an opening to give at least 50mm clearance all round the pipe and the opening masked with rigid sheet material to prevent ingress of fill or vermin. It is important that the void is also filled with a compressible sealant to prevent ingress of gas (see Diagram 7(b)).

Personally if you can achieve something like the back inlet gully (diagram in your post) with a 50mm waste run allowing for both movement & access on the up-stand under the sink & back inlet a 3m run it will be fine.
 
Last edited:

Reply to Kitchen island waste in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
116
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
120
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
199
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock