hello
After an engineer serviced our intergas boiler, the pressure was going down continuously. He told us that the prv was faulty and quoted us £200 to have it replaced, so we asked around and the last engineer told us that the pressure vessel, PRv are both faulty and the filling loop is leaking. He has not given me a quote yet but said that it is such a time consuming job that I might as well replace the boiler! Our boiler is 6 years old. It has been working with no problems. Any advice would be much appreciated.
 
It depends where the vessel is, some models they sit in a jig behind the boiler.... stupid idea but newer models they have moved it to the front...

If it's at the back then changing it is an arse and will often need a new flue kit....so by the time you've finished it's a new boiler kind of price.

When I've fitted one I've installed a separate vessel below the boiler on the return...that way it's an easy change.
 
if when you have run the c/heating then its cooled down you have to re fill it sounds like your ex vess could just have lost its presure hence it may just need to be represured. your prv may not be leaking as your boiler has gone over presure and passing the prv has let the presure out.
hope that makes sense.
 

Reply to Intergas boiler , vessel and PRV fault in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
203
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
324
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
276
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
183
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock