Hi guys, commissioned a Intergas ssyem boiler today. Work fine until later on it went to lock out code11?

I know the combi Intergas boilers require to set the parameters for a combi but does this boiler need to beset for a system boiler?

Nothing states in the manual about setting the parameters for this boiler..

I've checked the circulation sensors are all the way in there pockets.

I don't normally install Intergas boilers.

All help appreciated!
 
The likely issue if this is a new instal is insufficient circulation. If it is existing that has previously worked well, a defective sensor (S1 or S2) whichever is on circulation.

With respect to setup, the MI’s work through the required settings in a logical way. Are you sure that you are working from the installation and not the user manual?

Intergas technical support are very good if you are really stuck.
 
System isn’t air locked / you have flow ?
 
Would leave it a day and see if it returns if it does I would phone intergas up for maybe a chat and warranty call out
 

Reply to Intergas 30 sb fault code 11 in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
381
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
4
Views
177
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
117
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock