Hi guys, commissioned a Intergas ssyem boiler today. Work fine until later on it went to lock out code11?

I know the combi Intergas boilers require to set the parameters for a combi but does this boiler need to beset for a system boiler?

Nothing states in the manual about setting the parameters for this boiler..

I've checked the circulation sensors are all the way in there pockets.

I don't normally install Intergas boilers.

All help appreciated!
 
The likely issue if this is a new instal is insufficient circulation. If it is existing that has previously worked well, a defective sensor (S1 or S2) whichever is on circulation.

With respect to setup, the MI’s work through the required settings in a logical way. Are you sure that you are working from the installation and not the user manual?

Intergas technical support are very good if you are really stuck.
 
System isn’t air locked / you have flow ?
 
Would leave it a day and see if it returns if it does I would phone intergas up for maybe a chat and warranty call out
 