seymour

Morning and thanks for letting me join the group.
I'm having a problem with my Intergas 28/24 boiler. The boiler will fire up first time , reach the set temperature then switch off. When the temp drops and the boiler fires back up it won't restart and goes to fault code 4. I've taken the front cover off and have seen spark and flame at 1st fire up and attempted 2nd. After a couple of hours and Im guessing once it has cooled down the boiler will start again but fail at second .
The same process also happens if I just ask for hot water. (although hot water has been fine through out the summer)
Any help would be appreciated
thanks
 
Thanks for the reply Chris
I should have spent more time on the question. My plumber gas /safe engineer lives a fair drive away and i wanted to give him a bit of a heads up before he came. When I wrote remove the front cover I meant the white panel at the front which allows you to view the flame via the mirror on the upper left hand side, not the heat exchanger cover . Be sure I'm not about to tackle the problem myself .
Thanks
 
Yes I gathered you meant that cover, but it still forms part of the combustion circuit. As I said it could be a few things, which all need checking. If your engineer is familiar with Intergas boilers they should know what to check and what parts may be needed. If not then a fixed price repair from Intergas could be an option for you.
 

Reply to Intergas 28/24 boiler in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the outputs goes to a 2 port diverter prior to the Megaflo (I believe this is some safety feature). I have run into an intermittent problem where some...
Replies
5
Views
225
Hello Wondering if anyone can offer any clues please // Potterton Promax 18 // Had an E1 error code, repressurised via with filling loop // Boiler fires but now the pressure runs up from 1.5 mark in the green up to 2.5 in the red then flicks off. // Error code again // Once held in reset for...
Replies
1
Views
222
Hi I have a Vokera 15 vhe boiler and all has been running well for the last 6 months since moving in up until a few weeks a go. Boiler throws up a flashing 79 code. Try restarting the boiler straight away but I have to wait 10 minutes for it to cool down before it works. I reset the boiler...
Replies
23
Views
976
  • Locked
Hello, I have a ferroli falcon 2 boiler (yes it is pretty old). A few days ago the hot water started going hot and cold when running. Monitoring the boiler, the demand light works fine. When the water gets up to temperature every 10 seconds or so, the boiler stops for a fraction of a second...
Replies
3
Views
291
Hi All, Have a peculiar problem with my Gloworm Flexicom 30cx combi boiler, the main heat exchanger is getting red hot and fault coding on overheat even though the boiler and central heating is not on, i shut the boiler down for a while, clear the fault code and it will be fine again for...
Replies
21
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock