hi all,

i couldnt find exactly my issue, as i dont know what this design called.

im fitting a new flushing and filling mechanism. the filler element is the problem, as the pipe that connects to the cistern tap (the quick shut off one) is flattened?!

so its a half the thread, and the sides of the pipe are flat, hence water forces itself through the tiny spaces after everything is tightly screwed up. ive put in hard washers, soft ones, ptfe tape, nothing seals this.

im gonna attach a drawing quick. its only about the flattened sides of the pipe, no stress about the cistern or tap parts, they work fine.

is this a known design, or manufacturing issue? the unit cost a pretty penny. they say do not use putty. i would imagine the oil will disintegrate the plastic over some time.
 

Attachments

  • pipe.jpg
    pipe.jpg
    29.8 KB · Views: 21
Last edited:
Any chance of a picture of the item ?
 
Would say there supposed to be there have you tried an oring and just 1/4 turn when tight ?
 
Would say there supposed to be there have you tried an oring and just 1/4 turn when tight ?
I agree that the flattened side are by design to allow a spanner when tightening.

What are you trying to connect to the bottom? Can we get a pic? Needs to be a tap connector/braided hose. The seal is made at the bottom of the fill valve (horizontally across the flat face of the pipe/valve inlet), not at the threads. This seal will be made with a washer.
 
Would say there supposed to be there have you tried an oring and just 1/4 turn when tight ?
thanks, yes i have tried washers, hard ones too, quite tightly turned..water keeps coming... pictures attached, you can see the flattened side...

the first picture is the completed fitment, the water runs through where you see the ptfe tape. the pipe is screwed up right into the small shut off ball-valve, inside is a washer too...water still leaking once the valve is opened.
 

Attachments

  • IMG_20210729_181556.jpg
    IMG_20210729_181556.jpg
    268.7 KB · Views: 15
  • IMG_20210804_100106.jpg
    IMG_20210804_100106.jpg
    252.6 KB · Views: 17
  • IMG_20210804_100114.jpg
    IMG_20210804_100114.jpg
    234.1 KB · Views: 14
I agree that the flattened side are by design to allow a spanner when tightening.

What are you trying to connect to the bottom? Can we get a pic? Needs to be a tap connector/braided hose. The seal is made at the bottom of the fill valve (horizontally across the flat face of the pipe/valve inlet), not at the threads. This seal will be made with a washer.
thanks, yes you may have a point, its probably for a spanner, perhaps to counter turnforce. agree, the seal is made at the flat face, however can you believe i put a big enough washer there, but as you tighten the ball valve, it compresses the washer inside into the pipe! its the strangest thing. perhaps a fibre washer must be used..i dunno
 
Last edited:
You need a 'tap-connector' to seal to that plastic stem
The metal valve/tap you are using almost certainly doesn't have the required seating for a fibre washer as shown below
In the UK we could use this:
https://www.NoLinkingToThis/p/strai...V6oBQBh23lgCtEAQYASABEgKKyPD_BwE&gclsrc=aw.ds
Note how the fibre washer is held in place by the lip inside it. This makes a flat seal against the end of your plastic thread -the flat sides on the thread won't matter, as per previous postings tried to explain. All the 'seal' is provided by the washer being compressed by the two annular surfaces (which need to be flat and undamaged) - the thread shouldn't play a part as a seal, and you shouldn't need ptfe tape on it.
Can you find an equivalent locally? You will probably need to modify the pipework.
 
Last edited:
You need a 'tap-connector' to seal to that plastic stem
The metal valve/tap you are using almost certainly doesn't have the required seating for a fibre washer as shown below
In the UK we could use this:
https://www.NoLinkingToThis/p/strai...V6oBQBh23lgCtEAQYASABEgKKyPD_BwE&gclsrc=aw.ds
Note how the fibre washer is held in place by the lip inside it. This makes a flat seal against the end of your plastic thread -the flat sides on the thread won't matter, as per previous postings tried to explain. All the 'seal' is provided by the washer being compressed by the two annular surfaces (which need to be flat and undamaged) - the thread shouldn't play a part as a seal, and you shouldn't need ptfe tape on it.
Can you find an equivalent locally? You will probably need to modify the pipework.
thank you, ill have to try what else fits, as the brass pipe is cemented into the wall, and the cistern has of course remain in exactly the same space, so the pipework changing will be tricky. i will have to consider a braided hose and ball valve setup.
 
If you have scope to shorten or move the pipe slightly, and you can find an equivalent of the one below, then maybe this 'tap-adapter'/ service valve version (which I believe has a proper seat for a washer) could be fitted in.

 
If you have scope to shorten or move the pipe slightly, and you can find an equivalent of the one below, then maybe this 'tap-adapter'/ service valve version (which I believe has a proper seat for a washer) could be fitted in.

thanks for your help, yes, ill have to consider using other parts. i tightened everything up again, connected a hose pipe and it was fine. then i installed it all, the ball valve super tight on the threaded pipe, it still drips about 1 drop per hour. i will make a turn at the hardware shop again to check my options. thank you to all.
 
Have you tried twisting a piece of PTFE tape into a thread and wrapping it around where a a tap connector washer would usually go? I once had to do this as a fibre washer leaked - but this worked.
 
Have you tried twisting a piece of PTFE tape into a thread and wrapping it around where a a tap connector washer would usually go? I once had to do this as a fibre washer leaked - but this worked.
Thanks, I have not tried that... i will surely give it a try when i disassemble the whole lot again. so you mean, twisting it between your fingers, like a thin yarn, then lace it around the thread..clockwise of course.
 
Thanks, I have not tried that... i will surely give it a try when i disassemble the whole lot again. so you mean, twisting it between your fingers, like a thin yarn, then lace it around the thread..clockwise of course.
No. Twist it between your fingers to make a thread, but don't try to create a thread seal.

I've re-viewed your pics and think I see your problem though. It looks like that isolation valve has female threads and whoever has installed has tried to seal onto the thread of the plastic valve tail. This won't work. You need a tap connector fitting. Something along these lines

https://www.NoLinkingToThis/p/pegler-straight-service-valve-15mm-x/19933

that is designed to seal onto the end of the plastic. I was suggesting you might need to use PTFE 'string' instead of the red fibre washer that is normally supplied, but use the red washer if it works.
 

Reply to installing a new cistern in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, First post, be gentle! Anyway, here's my issue. I have a Roca The Gap D-Trit close-couple toilet with integrated macerator in my secondary bathroom. In all it's a great solution for a problem location for a bathroom. However, the cistern has a typical european style side inlet pipe, and...
Replies
9
Views
672
Hello! Im Martyn Im new here and have joined for some advice on a couple of things. Ive got an issue with a Mira mixer shower that has increasingly become harder to operate. The shower was installed before I moved into the house. Basically what happens is that I turn the shower on so there's...
Replies
1
Views
325
A
Hi all - hoping to get some advice here on a plumbing issue in our house. When we are showering / filling the bath and another appliance draws water (toilet cistern filling after flushing, tap being turned on or washing machine filling etc), the water pressure / flow to the other appliance...
Replies
4
Views
862
Azonic
A
Hey, forum friends! 👋 Excited to introduce Master Drain Ltd, your go-to expert for top-notch drain installation and repair services. Here's what sets us apart: 🔧 Seamless Installation: When it comes to drain installation, precision is key. Our skilled team at Master Drain Ltd ensures that your...
Replies
0
Views
351
Hi everyone, First time poster, go easy on me! My toilet cistern seems to be overfilling. It's a narrow plastic cistern (not important I imagine) and thankfully the overflow pipe is doing its job. The floating mechanism is working in that it's moving up and down, though it has a lot of...
Replies
4
Views