Hi All,



I have a Main Eco 30 Combi boiler I was fitted about 7 years ago, the whole pipe work is new and radiators.



There is one thing that annoys me on my boiler is that when ever is ignites it makes a small tiny explosive noise you can hear it from far 😫



I have so far replaced the electrodes since it was old and bent (it was working but I wanted to avoid it failing), the heat exchanger was hoovered and the seal was replaced, the diverter valve and actuator was replaced (since a small leak damaged it).

I have regularly flashed the water out using the drain point and running the boiler and keeping an eye on the pressure (the water is never too dark and flush it until it is clear water, I added some inhabitors, clean the filter out and took the air out of the rads, it is well balanced too.

I had to pressurise the extension vessel which is good now, on the same time I took the prv out and cleaned it very little dirt on it it’s working good, I also cleaned out the part in which condensation and other dirt accumulate.





There is one thing that annoys me on my boiler is that when ever is ignites it makes a small tiny explosive noise you can hear it from far 😫, you could describe it like a small delayed ignition 🤷🏽‍♂️



What would you recommend to check?
 

Reply to Ignition delayed/explosive Main Combi in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
122
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
62
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
221
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
224
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock