Discuss Ideal Logic Combi 24. Water is perfect for bathing a baby but not for shaving. in the Central Heating Forum area at PlumbersForums.net

Messages
8
Good Evening from sunny Clevedon. Heat Exchange was changed 1 year and 13 days ago. I fitted a new no flow thermister, which I was told would be the main suspect but has made no difference.
Any advice ? I have a big pan on the boil all the time for shaving and doing the washing up but I rather nice hot water came out the taps.

Cheers
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,435
Solutions
1
Have you tried slowing the flow of water out of the hot tap eg only open it 1/3
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,435
Solutions
1
Can you measure the flow rate out of said tap

Is it the same for all taps or just this one ?
 

scott_d

Plumber
Gas Engineer
Messages
5,664
It should increase the water temp by 35 degrees at 10 litres per minute.
Check cold water temp
Set hot tap to 10lpm
Check hot water temp
 
Messages
8
It should increase the water temp by 35 degrees at 10 litres per minute.
Check cold water temp
Set hot tap to 10lpm
Check hot water temp
So put 10lt bucket under bath tap . let HW run for a couple of minutes, then time it to fill and check temperature ?
 