Bear with me....
Bob goes to a job (CP12) System boiler with vertical flue. Working fine, gets flue analyser on it....Ratio 0.0700. Condemns boiler.
Boss goes round. Cant find problem. Not flue seals, fan, burner... Manufacturers called.
Technical say prob with flue. Flue installed (by other company years ago) found to be wrong flue. 100mm instead of 125mm.
Fit new flue. Ratio fine....
Now we have a few of these houses with these boilers on vertical flues. Boss doesnt want to replace all flues etc. Phoned Manufacturer who told him that "we shouldnt telegan the boiler just service it"??
Now tell me if im wrong, but even though a telegan isnt a vital part of the service. Now that weve found this problem. Surely we cant adapt the way we service the boiler just to make it pass the CP12?!?!?