Search the forum,

Discuss HRM Wallstar Oil Boiler - Advice please in the Plumbing Jobs | The Job-board area at PlumbersForums.net

yes I slipped up. Your figure is correct.
Yes please show me later and also explain where you got this method from and how accurate it is mate please.
 
The following is the heat balance method, I just use a shortened (my own) version above but it is 100% accurate.

L Litres = volume of cold water that must be added to 1 litre of hot water to give you the required mixed water temperature.
So: (1*80)+(L*12) = (1+L)*47
80+12L = 47+47L
33 = 35L
L = 33/35 or 0.942 litres
So 1 litre of hot water at 80C will give 1.942 litres of mixed water at 47C from cold water at 12C.
 
I presume the Firebird has a mixer to reduce the temp to ~ 65c and then the shower or whatever will reduce it to 50C but it doesn't matter as the stated conditions are water from a stored temp of 78 to water at 50C (from 10C) so the ratio is 1.7:1.

Thinking back again to the burner re firing at a store temp of 73C, if the probe picks this up very early in the draw off then you could be adding in energy early on so that will have the effect of increasing the thermal store so the 120 litres may actually be not too far off the mark as it would only need a additional ~ 2.5 kwh to achieve this but needs a bit more thought.

Think I may have finally come up with a reasonable calc for the above but is based on the boiler firing up almost immediately. The 78C high temp flow rate from the store will only require a flow rate of 20/1.7, 11.76 LPM from the store until it has fully depleted its 40 litres, the 35 kw boiler will also be heating the water to almost 53C at this flowrate so by the time the 40 litres at 75C is depleted then the store will be full of water at 53C = 43 litres at 50C, so 68 litres at 50C after mixing from the 78C store plus 43 litres at 50C with a little mixing gives a total of at least 111 litres at 50C?.
 
Last edited:
I'm going to trust your maths and judgement and say you could be correct.
Most oil combis state a maximum draw off at 40°c delta t, so there will come a time I assume and as I said above where the HW output temperature will start declining until the store is recharged.
 
It certainly will fall off because if the demand is kept at 20 lpm then once the first store is drawn off then the second store flow rate will rise to 20 LPM (practically no mixing) and once this is depleted (at 50C) the 35 kw boiler will only give a steady temp of 35C (35*850/20/60)+10), the flowrate must be reduced to 12.54 LPM, (35*860/40/60), to give a steady temp of 50C. In other words a flowrate of 20 LPM @ 50C will only be maintained for 5.5 minutes, 111/20, and the temp will then fall to 35C if not throttled in., I suppose that really isn't too bad as it will (almost) fill a bath or give a super power shower of 20 LPM for over 5 minutes. The key to the increased (temporary) flow rate is the burner cutting in almost as soon as there is a flow demand.
 
Last edited:
I think I saw somewhere that the Firebird store temp has a hysteresis of 5C so the burner may not cut in instantly on flow demand? Also one would think that the very nature of a store would allow a draw off of maybe 5 litres or so depending on where the probe is positioned. It would be interesting to get some feed from someone with a stored combi oil boiler.
 
All stats have a hysteresis but I couldn't tell you how wide it is on the thermistors or stats used. If you look at the flowchart for combi boilers you'll see a series of relays and stats and other components on PCB's. Of all my manuals stored show flow switches bringing on the boiler and pump when a hot outlet is opened. The store stat can also bring on the boiler to heat when no outlet is open to top up.
Another thing I will say is the newer firebird combis don't use a flow switch but instead another thermistor on the cold inletto PHX, which detects a change in temperature and brings the boiler on that way.
 

Reply to HRM Wallstar Oil Boiler - Advice please in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, I have a wallstar combi oil fired boiler. We got low on oil a couple of weeks ago but didn't run out. Since we've had our oil delivered the boiler won't fire up when hot taps are turned on so no hot water. The boiler fires up periodically to heat water but not when we turn on taps. I...
Replies
6
Views
615
We have an oil delivery booked for Friday but we ran out earlier today. We topped the tank with 150L from containers, bled the first boiler from the Allen key until the oil ran free and it fired up fine. Did the same on the second one but that had an E9 over temp error. We reset the thermostat...
Replies
4
Views
221
Heating and hot water is not working. Plenty of heating oil. I have replaced batteries in thermostat and it seems to be working ok, showing flame to call for heat, and the receiver seems to be working ok with green light, but heating is just not firing. I really am not sure what the problem is...
Replies
5
Views
309
Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for several hours before it will fire back up! Only to lock out again after 30/40 minutes! The boiler has had a new nozzle, coil and pump in the last 2...
Replies
19
Views
767
Hello Wondering if anyone can offer any clues please // Potterton Promax 18 // Had an E1 error code, repressurised via with filling loop // Boiler fires but now the pressure runs up from 1.5 mark in the green up to 2.5 in the red then flicks off. // Error code again // Once held in reset for...
Replies
1
Views
222
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock