Discuss HRM Wallstar 15/20 oil boiler cutting out in the Central Heating Forum area at PlumbersForums.net

Messages
8
I have an HRM Wallstar 15/20 boiler that is cutting out once or twice a day. It has a bubble in the oil pump suction hose. I have replaced the nozzle and oil filter element recently and checked and sealed joints in the suction pipe but bubbles still enter the transparent hose. In the past air had been sucked in through the filter bowl seal. Since then I changed the filter assembly. I suspect that air could be sucked in along the spindle of the fire valve/non-return valve. Could I be barking up the wrong tree? Could it be an ignition fault? It is a problem that has happened before and has come back to haunt me. Another factor is that the fuel level in the oil tank is low at the moment and could be affecting the boiler. Any ideas anyone?
 
6BE523B4-E2E6-4DC8-AF88-2B426619FE4A.jpeg


I have attached an image above. In the right green rectangle is where I’d suspect a possible suction leakage. The bottom left green triangle symbolises the recommended minimum fuel level. These pumps are capable of lifting fuel roughly 2.5m from lowest level of fuel line. if this is a problem you’ve encountered before then what fixed it last time? Really you should try and an engineer out, there’s only so much a DIYer can do
 
Thanks for your informative reply. The boiler was installed in 2006 and has suffered from cutting out at times. Earlier problems were caused by air being sucked in past the O-ring seal at the top of the oil filter bowl. The oil filter bowl was changed as the sealing surface of the filter bowl was porous. (a common problem with aluminium castings). A blocked fuel filter has caused the boiler to cut out in the past after the oil tank was replaced and moved. The tank is closer to the boiler now. Currently, I can see small bubbles drift up into the clear hose.

I measured the oil level as 250 mm from the bottom of the tank. The tank is being filled tomorrow so it will be interesting find out if that makes the problem go away for several months.
 
Thanks for your informative reply. The boiler was installed in 2006 and has suffered from cutting out at times. Earlier problems were caused by air being sucked in past the O-ring seal at the top of the oil filter bowl. The oil filter bowl was changed as the sealing surface of the filter bowl was porous. (a common problem with aluminium castings). A blocked fuel filter has caused the boiler to cut out in the past after the oil tank was replaced and moved. The tank is closer to the boiler now. Currently, I can see small bubbles drift up into the clear hose.

I measured the oil level as 250 mm from the bottom of the tank. The tank is being filled tomorrow so it will be interesting find out if that makes the problem go away for several months.

Once the oil tank is filled check to see if you're still seeing bubbles pulled up into the clear hose. If you still are then this suggests either a suction leakage or possible partial blockage, a vacuum gauge will help there. Many things can cause gases being separated from the oil if the vacuum was too high, ranging from too high a lift, blocked/partially blocked filters, crimped pipes, even the oil being too cold can cause this. Really you need to get to the bottom of the air/gases being pulled into the pump first.
 
Last edited:
Since the oil tank was filled on Monday the boiler has been working without cutting out so the problem would appear to be in the pipework between the oil tank and the oil pump. I will try to measure the pressure/vacuum at the oil tank, 2nd oil filter and oil pump suction hose.
 
Since the oil tank was filled on Monday the boiler has been working without cutting out so the problem would appear to be in the pipework between the oil tank and the oil pump. I will try to measure the pressure/vacuum at the oil tank, 2nd oil filter and oil pump suction hose.

From what you've said I suspect the problem was too low oil level, hence the original image I shared. Modern day pumps are capable of lifting oil quite a distance, even Riello pumps can lift a few feet but all pumps have a suction capacity. With your oil level low as it was and only atmospheric pressure on the bottom few inches then low pressure above the oil fill line will be quite drastic most likely causing these bubbles you saw being drawn into clear hose. When an oil line is subject to around 0.4-0.5 vacuum this is enough to pull gases from the oil which in turn make their way to the pump and you have nuisance lockouts.
If the burner is running fine then leave it be, dont start messing around with pressure and vacuum gauges.
 

Reply to HRM Wallstar 15/20 oil boiler cutting out in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for several hours before it will fire back up! Only to lock out again after 30/40 minutes! The boiler has had a new nozzle, coil and pump in the last 2...
Replies
19
Views
769
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from the loft water reservoir tank (which also feeds the cold water taps in the bathroom & the WC cistern). There is an expansion vessel attached to this...
Replies
0
Views
474
Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed gas could be burned with a blue flame and the water was acidic (pH 5.5). Since then system has been chemically flushed (it was not too bad) and the...
Replies
1
Views
202
I have a "Firebird Envirogreen Condensing Combi Oil Boiler 26kW" a part has went and I can't find it anywhere, I was at every plumbers merchant near me but they all need to ring Firebird who are closed till next week. I wonder if anyone can help me find this part please? It's a pressure sensor...
Replies
2
Views
371
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not been serviced in a long time and oil filters were bunged up as was the nozzle. I decided to service it with hopes it was simple starving of fuel from...
Replies
1
Views
606
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock