I have a client with grant vortex combi 21 condensing 2007. Looks similar to be new vortex 21e but the control panel is different. Has a few seperate circuit boards and clear relays.
The fault is that it just stays on when central heating on until high limit kicks in. I've checked for trapped air (auto air vents) ok.
The hot water when used runs a bit then boiler switches off when stored hot water is hot as it should.
I want to test the temperature stat as when turned you can not hear any click at temperature change when rotating. This control knob seems to go through to a circuit board. (looks like MPCBS54 ) . Question is how do I test this to see this Stat is working OK..?
 
Took a bit of working out but looked like someone had switched the thermistors sensors for hot water and heating in the wrong phails holders, The thermostat seems to be working. Hot water pump runs a while (and rattling )before stopping. Could the rattling cause cavitation and air getting trapped at the top at the non venting Auto air vents... Fingers crossed
 

Reply to How to test per 2007 grant temperature controller in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
82
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
304
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
53
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock