I have tried all the tests I can think of and nothing seemed out of the ordinary so trying this now. No one seems to have any other answers - desperate times!! My wife is giving me so much grief I am doing anything at this point! Lol
 
Messages
1,934
Don't know if fitting a new complete motorized head instead of just the synchron motor would make any difference or not. In the meantime suggest fitting (again) the motorized head from the CH to the HW and wire it up by removing/using the wires from the "old" HW head, let the wires disconnected from the other actuator and see what happens.
 
Messages
30
Disconnect the orange wire and see what happens or what shouldn't happen.
I disconnected the orange wire and turned the power on. The MV still moved around and engaged the switch but the boiler didn’t fire up (I guess that’s what the orange wire does :))
 

Attachments

  • EC715DD4-6D51-4A63-9A61-D482882E00B2.jpeg
    EC715DD4-6D51-4A63-9A61-D482882E00B2.jpeg
    370.1 KB · Views: 14
Messages
30
Don't know if fitting a new complete motorized head instead of just the synchron motor would make any difference or not. In the meantime suggest fitting (again) the motorized head from the CH to the HW and wire it up by removing/using the wires from the "old" HW head, let the wires disconnected from the other actuator and see what happens.
When I swap the heads over and the wiring then the same thing happens. But before I changed the wires over I tried just swapping the heads. So basically to get the Hot Water is now controlled by the Heating side of the programmer - Doing this solves the issue - it works as it should - to get the MV to operate I had to turn on the HG60 and the programmer on and then the MV kicked in as normal to turn the hot water on. Brilliant! But then the other valve opens the heating valve and turns the Heating on without being asked! So must be a wiring issue? Even though I haven’t moved any wires around before the issue started? I posted a pic of the wires in the post earlier
 
Messages
30
Don't know if fitting a new complete motorized head instead of just the synchron motor would make any difference or not. In the meantime suggest fitting (again) the motorized head from the CH to the HW and wire it up by removing/using the wires from the "old" HW head, let the wires disconnected from the other actuator and see what happens.
When I swap the heads over and the wiring then the same thing happens. But before I changed the wires over I tried just swapping the heads. So basically to get the Hot Water is now controlled by the Heating side of the programmer - Doing this solves the issue - it works as it should - to get the MV to operate I had to turn on the HG60 and the programmer on and then the MV kicked in as normal to turn the hot water on. Brilliant! But then the other valve opens the heating valve and turns the Heating on without being asked! So must be a wiring issue? Even though I haven’t moved any wires around before the issue started? I posted a pic of the wires in the post earlier
 
Messages
30
I have taken the fronts off all the controls but the Lee is still 240v on the orange and the grey cables and when I turn the far right switch on or off this turns the hot water on and off without any controls. Is there a wire I need to move etc?? I have tried it with the MV head from the heating valve and re wired it but it does exactly the same thing so can’t be the head as the Heating head works fine when it’s on the Heating.
 

Attachments

  • image.jpg
    image.jpg
    366.5 KB · Views: 5
Messages
1,934
Have you checked the wiring at the ST9400A controller in case there is a extra permanent live connected by mistake to the "HW Off" which is used for a Y plan configuration or something along those lines.
 
Last edited:

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,435
Solutions
1
You have a bad port valve or one permanently calling do you have any voltage on the browns on the port valve wires ?
 
Messages
30
Need to test no point in throwing parts at it
i have taken the program unit and the HG60 module off. The power is on. you should make out the numbers behind the wires. with the black wire on the tester in space 3, I have 240v in lines 1, 7, 8 and 0. The HW is on and won’t switch off. Even though the controls are removed.
 

Attachments

  • 9E4621D6-316E-4540-94E4-402EE2643172.jpeg
    9E4621D6-316E-4540-94E4-402EE2643172.jpeg
    495.1 KB · Views: 5
Messages
30
Have you checked the wiring at the ST9400A controller in case there is a extra permanent live connected by mistake to the "HW Off" which is used for a Y plan configuration or something along those lines.
I notice that this is not how it says it should be wired on the back of the program box
 