Discuss Hot water pump runs continuously in the Central Heating Forum area at PlumbersForums.net

Messages
8
I have a Potterton Precision boiler fitted by British Gas 8 yrs ago. All good up to now but in the last few months it has failed to come on a number of times when required by the thermostat. I have had to press the reset button. The pump has also recently started to show it is running at low power 24/7 ( ie between 4 and 6 watts). Had a Corgi engineer to look at it - he says he has sorted the ignition problem (which I shall have to wait and see if he is right) but he says the pump should be on all the time with my make of boiler. I disagreed with him over this as I think it should just run on for a short while after the finish of an ON period. Can anybody advise me if I am correct please?
 
If you have a external circ pump can you measure the voltage at the motor terminals while drawing this low power and also have you got a A rated (Smart) circ pump?
 
What are you resetting? If your pump is failing, or has failed, and if you’re resetting an overheat situation then your pump could well be knacked.
 
There is a rest button on the boiler - I used this to get the boiler to ignite when it failed to do so when demanded by my CH thermostat. The pump is external - a Grundfos - it has a range of power settings but I have is set on AUTO. If I wind it up to the max setting (50w) it still runs 24/7. When the thermost calls for heat, everything runs as it should. Sorry I don't know how to measure the voltage.
 
So with all thermostats off and timer to the off does the pump run ?
 
Yes there’s a fault there something is backfeeding the pump or there water flowing through the pump
 
There is a rest button on the boiler - I used this to get the boiler to ignite when it failed to do so when demanded by my CH thermostat. The pump is external - a Grundfos - it has a range of power settings but I have is set on AUTO. If I wind it up to the max setting (50w) it still runs 24/7. When the thermost calls for heat, everything runs as it should. Sorry I don't know how to measure the voltage.

If wired via the wiring centre and not from the boiler then possible zone valve micro switch problem or unlikely but may have been wired directly from a independent source.
Also the Grundfos Auto adapt mode rarely, if ever works properly and the power output rarely rises above 9 to 12 watts which normally gives inadequate water circulation, whatever mode you select IMO should result in a power output of 14 to 25 watts, you did say you had ignition problems which should be unrelated except the boiler had cut out on overheat but then should give a fault code.

Edit: just saw your post above so maybe possible that if this pump was retrofitted that someone did connect it independently but you would probably have noticed this previously.
 
Last edited:

Reply to Hot water pump runs continuously in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
202
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock