Is there any advice on using Honeywell Evohome with 2 zone heating. Honeywell support are pretty useless and give conflicting advice. They suggested I ask my installer (but my installer suggested I ask Honeywell). I found a support article on the Honeywell Resideo website by Googling "How-to-control-more-than-one-heating-zone-valve-with-evohom". This seems to suggest binding the two port valves (which is not what I want to do).

Ideally I would have HR91 Radiator Controllers on some but not all rads. This doesn't seem like it is supported. I'm not even clear if I can have HR91 Radiator Controllers on all rads in one zone but not the other.

If Honeywell Evohome does not support dual heating zone systems well then does any other system?

It seems worrying that Honeywell don't seem to have a clue how to support this given the fact that Building Regulations Part L 2010 mandate two zones. Even if Evohome makes two zones redundant, it does not seem sensible to tell people just to bind the zones.
 

Murdoch

Esteemed
Res.Electrician
Messages
1,109
I don’t know this for sure but I suspect that you’ll need to make sure both zone valves are always open.

each trv will call independently for heat so the heating needs to be able to flow to anywhere (if that makes sense)
 

samwardill

Messages
9
Honeywell Evohome Installer here -

Not sure what you're trying to achieve? You want HR91s in one zone, but not the other?
Why not? Even if I had TRVs throughout it seems crazy that the system can not differentiate where they are and only call for heat to the zone where the TRV is that needs heat.
 

Murdoch

Esteemed
Res.Electrician
Messages
1,109
I think you will find that it’s Evo Home for everything or nothing. I doubt you’ll be able to mix and match zones
 

EvilDrPorkChop

Esteemed
Plumber
Gas Engineer
Messages
1,239
Why not? Even if I had TRVs throughout it seems crazy that the system can not differentiate where they are and only call for heat to the zone where the TRV is that needs heat.
It was a simple question of what you were trying to achieve - as you didn’t explain fully in your original post!
 

samwardill

Messages
9
It was a simple question of what you were trying to achieve - as you didn’t explain fully in your original post!
I’d like to control one zone of my house using room based Trvs and the other using a zone thermostat. Even if I ultimately decide to instal smart trvs everywhere , I want the system to use the zones to send heat to the zone that is calling for heat .
 

EvilDrPorkChop

Esteemed
Plumber
Gas Engineer
Messages
1,239
I’d like to control one zone of my house using room based Trvs and the other using a zone thermostat. Even if I ultimately decide to instal smart trvs everywhere , I want the system to use the zones to send heat to the zone that is calling for heat .
Yeah you can do that.

Zone 1 with TRVS - remove or lock open the Motorised valve. Disconnect electronically.

Zone 2 - set up as an extra zone controlled by Zone Valve with an additional stat or just the panel as the stat.
 

samwardill

Messages
9
Yeah you can do that.

Zone 1 with TRVS - remove or lock open the Motorised valve. Disconnect electronically.

Zone 2 - set up as an extra zone controlled by Zone Valve with an additional stat or just the panel as the stat.

I think I'll get a Drayton Wiser. They have a system that is designed to work with two heating zones (using the motorised valves).
 

Reply to Honeywell Evohome with 2 zone heating in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar threads

M
Part of the problem is getting a Evohome Specialist to look at an existing system, they just aren't interested near me. Thanks for your help...
Replies
13
Views
404
Mark8par
M
R
Topic has recently been discussed here: https://www.plumbersforums.net/threads/replacing-honeywell-cm921.127707/#post-1155638
Replies
1
Views
71
Chuck
C
P
Perhaps try running just one of HR92s in the main bedroom zone, they could now be interferring with each and causing the drop.