Hi
I have a recent issue in that I can only get heat upstairs or downstairs but not to both. And when I do put just the downstairs heating on, the two furthest away radiators struggle to warm up even when the other radiators downstairs are turned down. Also, when the hot water comes on both upstairs and downstairs can't heat.

I have tried balancing and cleaning the system (cleaned all downstairs radiators via a hose outside and put in Fernox F3 cleaner) but that hasn't worked. I have also opened up the pump (Grundfos Alpha2 15-60 130) and ensured that it was spinning freely, which it was.

Two plumbers have come to inspect it - the first cleaned a few parts in the boiler along with suggesting putting in the cleaner to get rid of sludge as they thought the boiler and pump were working ok.

The second plumber suggested a stronger cleaner be used i.e. Fernox F5.

The system has a Spirotech MB3 fitted on the outflow from the boiler and before the pump - I know it is in the wrong place! Having figured out what it was, I cleaned it for the first time having to poke a cotton bud up through the hole to make the water flow out as it was so clogged up! It seems to be pulling black water every few days.

So, I am looking for suggestions on my next steps to resolve this heating issue. I have been thinking about the following options:

1. Just put Fernox F5 into the system and let it run for a week then drain.

2. Put Fernox F5 into the system and use a power flush machine.

3. Same as option 2 but use a magnacleanse machine to avoid extra pressure which might burst fragile pipes. This will be the most costly option as I will have to purchase the magnacleanse machine as I can't find any company that hires them out!

4. Replace the pump as even though it might be spinning freely, its strength may have diminished over time. I did notice that after agitating the pump the inflow pipes to the radiators downstairs did get hotter.

I am leaning towards Option 3 followed by Option 4 if Option 3 doesn't work.

Any advice is welcomed!

Thanks

Vik
 
Before this problem, how was your heating. Was everything warning up nicely from top to bottom? I'm thinking pump on this one.

What system is it?

I wouldn't recommend trying chemical after chemical though.
 
The two radiators not heating up downstairs have always been an issue but they did get hot on occasions. The others downstairs were a little cooler nearer the bottom. That's why I took them off to clean them through with a hose. Upstairs has been fine.

But yes, we were getting heat upstairs and downstairs and didn't notice a fall off in heat when the hot water came on.

Now if both upstairs and downstairs are calling for heat, downstairs remains stone cold whereas upstairs is fine.

When I switch the pump (Grundfos Alpha 2 15-60 130) to Autoadapt mode it just stays at about 5 watts although I think it has always done this but I could be wrong! In any case, 5 watts isn't enough to heat the house so the Autoadapt isn't working as it should!

It's a gravity fed system.
 
Last edited:
The two radiators not heating up downstairs have always been an issue but they did get hot on occasions. The others downstairs were a little cooler nearer the bottom. That's why I took them off to clean them through with a hose. Upstairs has been fine.

But yes, we were getting heat upstairs and downstairs and didn't notice a fall off in heat when the hot water came on.

Now if both upstairs and downstairs are calling for heat, downstairs remains stone cold whereas upstairs is fine.

When I switch the pump (Grundfos Alpha 2 15-60 130) to Autoadapt mode it just stays at about 5 watts although I think it has always done this but I could be wrong! In any case, 5 watts isn't enough to heat the house so the Autoadapt isn't working as it should!
I think its amazing how well informed some if our respondents are now a days
it makes problems so much easy to look at
chking
 
Aye 15mm which is good. But them alpha pumps can be too smart for their own good.

Please correct me if I’m wrong but are we suggesting that the system is riddled with black iron oxide and this increase in pressure due to resistance is causing the pump to modulate, which in turn is not providing enough KPa to overcome and therefore not get heat everywhere?
 
Please correct me if I’m wrong but are we suggesting that the system is riddled with black iron oxide and this increase in pressure due to resistance is causing the pump to modulate, which in turn is not providing enough KPa to overcome and therefore not get heat everywhere?

Probably! What's the best way to resolve the issue?
 
Have you or did the plumber remove the pump head and check the impeller was clean? I've seen loads of impellers and pump bodies that have been clogged up which obviously restricts the flow of water.
 
I’m reluctant to comment as I’m not an installer like SimonG and these other guys. I understand these things and how they work however I’m a humble hoover man (oil fired appliances). If the system IS infected with large amounts of sludge (black iron oxide) then a proper power flush is where I’d start, bare in mind this is not an hours job. The system should be flushed as a whole, then each rad individually and then the system as a whole again. Proper chemicals should be used and again larger systems could take considerably longer.
 
Have you or did the plumber remove the pump head and check the impeller was clean? I've seen loads of impellers and pump bodies that have been clogged up which obviously restricts the flow of water.
I did the same as this guy:


Not sure if that's what you mean. The impeller was moving freely both ways and the water coming out was clear.
 
I’m reluctant to comment as I’m not an installer like SimonG and these other guys. I understand these things and how they work however I’m a humble hoover man (oil fired appliances). If the system IS infected with large amounts of sludge (black iron oxide) then a proper power flush is where I’d start, bare in mind this is not an hours job. The system should be flushed as a whole, then each rad individually and then the system as a whole again. Proper chemicals should be used and again larger systems could take considerably longer.

Sounds sensible - I can hire a flush for the weekend.
 
I managed to get to the impeller - all bar one of the channels for water were clogged up. Having unclogged these the pump is now running at 36watts vs a previous 25watts. When upstairs and downstairs and hot water are calling for heat, only upstairs and hot water are getting any. If it's just hot water and downstairs calling for heat, then it's just hot water which gets any. If it's just downstairs calling for heat, then it gets heat but those two furthest radiators are still an issue.

So, no change apart from the pump is now able to use more energy.

I am inclined to think that a power flush is the next step. Any thoughts?
 
Last edited:
A permanent magnet should be installed on return back to boiler anyway to help. You would benefit from a proper power flush as well though as any hard set sludge in system may not budge and circulate back to magnet to extract. I once saw a system with V,C,P not right and all pipework was riddled with sludge, 22mm pipe had an internal bore of about 2-3mm it was that bad. In the end the guy said just rip out and start from fresh.
 

Reply to Home heating issue - Upstairs and downstairs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
74
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
89
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
200
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
354
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock