Azz

Messages
16
customer complaining regarding heating running on low heat around 40.c at most, showing on front panel.
Have push up tempreture to maximum of 65c but boiler just dosnt seem to go beyond 40.c.
Hot water works fine.
Its a small flat with 3 radiators 1 large and 2 medium size, have carried out system flush as water was very dirty but has not made much difference.
By removing actuator motor and turning hot water tap on, the heat will go on heating side perfectly reaching tempreture of 80.c and all rads are piping hot, which takes out any doubts about blockage.
Have also replace flow and return ntc's with no effect
The other trouble is there is no technical help with heatline as they seized to exist.

Any help would be much appreciated.
 
If no blockages then it a diverter problem these boilers are cheap and nasty but very expensive on parts obviously the heating should not come on when hot tap is operated. As above I would consider a upgrade. Kop
 
Thanks for the response. Heating does not come on when hot water is on or get heat on the flow beneath boiler. As previously stated that when the actuator motor ir removed and hot water tap on is when central heating gets fully hot, as actuator motor pushes diverter pin for hot water and opposite for heating.
Have also replace pcb recently as heating was not coming on at all but after pcb chage it comes on but upto 40.c

This is a push button for tempreature adjustment which corresponds with digital screen so cant be a potentiometer.

Customer spent a lot of money on this boiler and feels gutted to require a change as im sure its around 5 years old.

Thanks
 

Reply to Heating issue with heatline capriz plus 24a in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

A
I have a heatline vizo 24 combi boiler that starts up for a few seconds and then shuts off. This happens with both hot water and heating. If left all overnight or all day it will work first time and stay on. If tried again soon after the problem comes back.
Replies
3
Views
521
Deleted member 120897
D
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd, London. Job Description: Problem: The boiler is not providing heating under normal conditions, although hot water supply is fine. Interestingly...
Replies
1
Views
384
M
I've got a heating boiler which heats up the water in a tank located in a cupboard upstairs and then from there I get hot water & hearing. I get hot water ok but the heating doesn't come on when turning the thermostat to a higher temperature. I've got a 2 way motorized diverter valve which would...
Replies
2
Views
640
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open vented system to sealed / pressurized system, new pump ( UPS3 Grundfos ) all new plastic pipework ( extending ) the 22mm feed and return pipes so no...
Replies
9
Views
992
So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to give a full picture but let me know if ive missed anything. I have a Baxi Avanta 25h heat only boiler. Works fine. Unvented 300ltr megaflow. Stated...
Replies
1
Views
145
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock