Good morning, was hoping someone could tell me the minimum height the header tank needs to be above the hot water (indirect) cylinder. Many thanks in anticipation. Sam
 
There is no real height requirement other than it must provide enough head pressure to allow the top most parts of the system to fill with water, which would presumable be the upstairs rads not the cylinder coil.

The issue is more to do with the correct pipework design & installation, all intended to keep as much of the system under positive pressure when the pump is running at the same time ensuring that when it starts up water is not pushed out from the safety open vent pipe into the cistern. Lastly as much as possible of the extra water created when the system is heated remains in the within the cold feed as water moving up into the cistern when hot & then back into the circulating water when cold would introduce oxygen & promote corrosion.
 
F&E tank supposed to be at least a metre above the highest circuits in your heating system.
But extra long feed pipe is often better to ensure less air ingress into system.
But it depends on how it is all piped on your system.

You would be best to have your heating system sealed if it is gas or oil system.
There is very little cost to this normally.
The system will need to be sound though, - no slight weeps anywhere and radiator valves all with proper sealing glands, so no pressure loss
 
Look, what you should consider is how high you can locate your tank...not how low ..done the odd one over the years at min. spec height and they worked but the performance really was rubbish
in my opinion...or just rip it all out and go unvented
chking
 
Hiya Yd

he said at the beginning it was the high level cold water then it got mixed up ..(as usual) into the f&e ..I wonder which one it might be ...happy days my Sunday dinner is wafting up to my workshop ...beef today
Rob Foster aka centralheatking

Thats why i edited Rob. Skimmed the bulk of the thread only ;)
 

Reply to Header tank/Hot water cylinder in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
59
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
168
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock