Hi, I have a Grundfos UP15 42RUC7 circulator which doesn't appear to be working. the impeller moves freely when I spin it manually but when there is power tot he device all I hear is humming but the impeller doesn't turn even though it does not appear to be stuck. Also, oddly I can not find my model # anywhere for this Grundfos. The closest I have found is UP15-42BUC7 but you can see clearly in the picture I have attached that my model is an "R" and not a "B". Any help would be appreciated. As mentioned - power appears to be at the unit and the impeller is not turning even though I can spin it freely by hand - thanks

IMG-8613.jpg
 
Nope-but wouldn’t the impeller still spin even if the capacitor was faulty with power running to the unit and you can audibly bear the unit humming?

A humming/buzzing noise is typical audible sound of a cap failed or a seized motor. The motor will spin by hand as it is with a failed cap but trying to start a single phase motor without an auxiliary winding and a cap is impossible, once rotating it would be fine but not to start.
 

Reply to Grundfos water circulator not circulating in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
90
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
235
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
66
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
222
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
135
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock