Didn't notice attachments before.......if the arrow on the pump body is pointing downwards then the pump is installed correctly.
Thanks John. Valves seem to be fully open. Can't see an arrow on the pump body. Where should I be looking?
Does the setting on our boiler that I mentioned have any bearing (3-4 on range 1-5/max) on things?. Likewise the thermostatic radiator valves?
 
Settings on boiler and TRVs are fine.

The pump arrow is on the pump body directly behind o the plug socket and is pointing upwards, probably downwards in your installation (on right hand side).


Can you also get a close up photo of the arrowed area in attachment.

And also around the pipework runs from the mid position valve to the cylinder coil flow and return etc.

1635254503631.png
 

Attachments

  • pipework.jpg
    pipework.jpg
    504.8 KB · Views: 17
Last edited:
Settings on boiler and TRVs are fine.

The pump arrow is on the pump body directly behind o the plug socket and is pointing upwards, probably downwards in your installation (on right hand side).


Can you also get a close up photo of the arrowed area in attachment.

And also around the pipework runs from the mid position valve to the cylinder coil flow and return etc.

View attachment 65156
Arrow on pump was quite difficult to access and take snap of but have attached the best I could get. It is pointing down.

Also attached close up arrowed.

Many thanks
 

Attachments

  • pump_arrow.jpg
    pump_arrow.jpg
    547.6 KB · Views: 13
  • close_up.jpg
    close_up.jpg
    325.2 KB · Views: 11
So pump is correct, the arrowed item is a mini ball valve by pass which is partially opened, can't see any reason why CCII shouldn't give perfectly acceptable flow rates compared to CCIII, it should give ~ 90%. so still points to pump problems IMO.
Its a bit surprising that your engineer didn't try out any other modes as most would settle traditionally for CCII even if they knew nothing about the other modes.

Also point out to him that the UPS3 CCII is more powerful than the Selectric CCIII.

Did your engineer make any other changes apart from the new pump & mid position valve?.

So, Stephen, If it were my installation, I would contact him and inform him of results, can't offer any other words of wisdom I'm afraid.
 
Last edited:
So pump is correct, the arrowed item is a mini ball valve by pass which is partially opened, can't see any reason why CCII shouldn't give perfectly acceptable flow rates compared to CCIII, it should give ~ 90%. so still points to pump problems IMO.
Its a bit surprising that your engineer didn't try out any other modes as most would settle traditionally for CCII even if they knew nothing about the other modes.

Also point out to him that the UPS3 CCII is more powerful than the Selectric CCIII.

Did your engineer make any other changes apart from the new pump & mid position valve?.

So, Stephen, If it were my installation, I would contact him and inform him of results, can't offer any other words of wisdom I'm afraid.
Hi John. Firstly thank you so much for all your words of wisdom. You really have gone above and beyond to help and it is very much appreciated. It makes a huge difference to us to be able to call the engineer back knowing what it is reasonable to expect from the UPS3 in general and particularly, as you say, that UPS3 CCII is more powerful than our old pump - which supplied the system perfectly well for many years.

We are not aware of any other changes he made apart from fitting the Grundfos pump (and new pump valves), Drayton mid position valve and rewiring the (previously incorrectly wired) existing Drayton controller. He also drained and refilled the system.

Can I just ask couple more things before signing off?

The engineer initially quoted for a Honeywell mid position valve but actually supplied a Drayton. We didn't query this as the controller is a Drayton. Is this likely to have any bearing on the issue?

I only noticed after our last exchange of messages that, after I tried different pump settings and returned it to CCIII, one radiator that had previously been hot was lukewarm and one had not come on at all (both downstairs). I turned the boiler controller to 5 and both radiators came on. Any implications there?

And finally a (probably) really stupid question... should the circulating pump be constantly running when only hot water is selected on the controller?

Once again, many thanks for all your help John, you have been brilliant!
 
Mid position valve make should make no difference.

Don't think changing the boiler flow temperature should have any effect on the pump operation.

Pump should be constantly running with HW only selected as long as the cylinder stat is requesting heat.

Let us know how you get on.
 
Mid position valve make should make no difference.

Don't think changing the boiler flow temperature should have any effect on the pump operation.

Pump should be constantly running with HW only selected as long as the cylinder stat is requesting heat.

Let us know how you get on.
Thanks so much John. Will do.
 
Mid position valve make should make no difference.

Don't think changing the boiler flow temperature should have any effect on the pump operation.

Pump should be constantly running with HW only selected as long as the cylinder stat is requesting heat.

Let us know how you get on.
Good morning John

Not the response I imagine either of us expected me to post I’m afraid…

Apologies for the length of this post but as succinctly as possible…
  • Engineer returned and suggested that running the pump on CCIII continuously was fine
  • We said CCIII was noisy & resonating and that CCII was more powerful than our old pump
  • Engineer said he would balance the radiators (but only adjusted 4-5 rads)
  • Ran quietly on CCII for a couple of hours after he left but 2 upstairs radiators soon cooled
  • Following morning successfully ran on CCII for an hour on water only – water very hot in < 1 hour
  • Switched to heat (CCII) - only 3 upstairs rads fully hot, 5 downstairs warm only and 2 upstairs cold
  • Within an hour boiler was mostly off and all rads cooling
We are waiting for the engineer to return but in the meantime we have tried various combos of heat only/water only/heat+water in both CCIII and CCII and have concluded the following:
  • Since engineer ‘balanced’ the radiators 2 upstairs rads do not heat (1 cold/1 lukewarm) even in CCIII
  • Pump and system is still noisy on CCIII (vibration can be felt through feet on floor outside airing cupboard)
  • On CCIII in heat only mode the 8 radiators that do work get very hot
  • Boiler continues to repeatedly fire up after the 8 working radiators have reached full heat
  • On CCIII in water only mode water in the tank is fully hot (from cold) within 30mins
  • On CCIII in heat+water mode 2 downstairs rads failed to reach full heat & water took 60mins to get hot
  • Running heat+water seems to result in air getting into the system and the pump pulsing
  • On CCII in water only mode system successfully fully heated the tank in < 1 hour
  • On CCII in heat only mode system will run for an hour or so but ONLY AFTER rads have fully heated on CCIII first then switched to CCII
  • Running on CCII after system had cooled for an hour (after running heat+water on CCIII) the downstairs rads failed to reach full heat after 90mins, pump started pulsing and the rads started to cool
  • 2nd attempt to run heat only on CCII after the system had fully cooled resulted in pulsing after only 20-25 mins see attached video
  • Switching on heat in CCII mode the morning after the above resulted in spluttering from the pump and the sound of rushing water see attached video
Summary:

We can run in CCIII in either heat only or water only but if we try to run heat+water together in CCIII or run other than water only in CCII we get problems that seem to be related to air getting into the system.

Could this be caused by a problem with the mid-position valve?
 

Attachments

  • Grundfos_pulsing.mp4
    5.3 MB
  • Grundfos_splutter.mp4
    11.8 MB
Its most likely that the air is a result in running in CCIII which is 6.4M, CCII should definitely be more than enough but obviously isn't. If we assume that the pump isn't faulty then I would shut that by pass fully, (see closeup.jpg post 38) put a mark opposite the slot ends and then either use a screwdriver or a allen key to turn the slot fully horizontallly and see if pump still noisy, even if it is retry it on CCII.

If you have 2 cold water storage tanks in your attic, check that the smaller of the two has water in it, you didn't say I think that you had this small tank but did say you didn't have a pressure gauge.
 
Last edited:
Its most likely that the air is a result in running in CCIII which is 6.4M, CCII should definitely be more than enough but obviously isn't. If we assume that the pump isn't faulty then I would shut that by pass fully, (see closeup.jpg post 38) put a mark opposite the slot ends and then either use a screwdriver or a allen key to turn the slot fully horizontallly and see if pump still noisy, even if it is retry it on CCII.

If you have 2 cold water storage tanks in your attic, check that the smaller of the two has water in it, you didn't say I think that you had this small tank but did say you didn't have a pressure gauge.
Thanks John

Yes small tank is full & we don't have a pressure gauge. Just to be 100% sure I am adjusting the correct thing - we are talking about the attached valve, correct?

Interesting that you say that the air is a result of running in CCIII. I spoke to someone from Grundfos who told me to run it in CCIII to vent the air after it started pulsing in CCII.

Do you think that the pulsing and spluttering in the previously attached videos is indeed air in the system? Could the pump actually be faulty?

Thank you so much again!
 

Attachments

  • by_pass.jpg
    by_pass.jpg
    306.8 KB · Views: 3
That's the valve alright.

Running that pump in CCIII in a OV system will IMO lead to air ingress, its OK in a sealed system.

Are you getting any air from any of the rads etc?, also look into the small tank and see if any signs of agitation etc, while you are watching get somebody to start/stop the boiler and see if any water coming from the vent., also feel the cold water outlet from the tank and see if its hot. Is the tank clean?.
Can't really say if the pump is faulty or not, there may be a blockage somewhere in the cold feed, can you see where it joins the system?., if the system was drained down recently and refilled then unlikely that its blocked.
 
That's the valve alright.

Running that pump in CCIII in a OV system will IMO lead to air ingress, its OK in a sealed system.

Are you getting any air from any of the rads etc?, also look into the small tank and see if any signs of agitation etc, while you are watching get somebody to start/stop the boiler and see if any water coming from the vent., also feel the cold water outlet from the tank and see if its hot. Is the tank clean?.
Can't really say if the pump is faulty or not, there may be a blockage somewhere in the cold feed, can you see where it joins the system?., if the system was drained down recently and refilled then unlikely that its blocked.
Many thanks again. The engineer turned up unexpectedly this afternoon and decided to change the pump. Will report back as soon as we have had a change to run it thoroughly.

Hadn't yet tried the by pass. Mentioned it to the engineer but he said it was seized up in that position. Fingers crossed!
 
Reading this with interest I was thinking that the radiators might need balancing, if some rads don't get hot on CCII then then their lockshield valves might need opening. It sounds like your man started this but didn't finish, it can take several days to complete, there is a sticky thread at the top of the forum, I would give that a go.
 
FYI I have a grundfos pump, a but different to yours but it has various modes including some constant speed modes I, II & III, I run mine on speed II as like you found that III was too noisy. I have 14 radiators and this setting works perfectly for me.
 
Agree, I have 10 rads (no balancing), OV system, on a 4.4M PP setting (Wilo Yonos Pico) which gives ~ 14LPM @ 3.2M.
The UPS3 flows 18.3LPM @ 6.3M on CCIII & 18.3LPM @ 5.0M on CCII.

As a matter of interest what model Grundfos do you have?.
 
Agree, I have 10 rads (no balancing), OV system, on a 4.4M PP setting (Wilo Yonos Pico) which gives ~ 14LPM @ 3.2M.
The UPS3 flows 18.3LPM @ 6.3M on CCIII & 18.3LPM @ 5.0M on CCII.

As a matter of interest what model Grundfos do you have?.
Hi John

So it seems that you were correct when you deduced that it was most likely a faulty pump back in post #32! Just a pity that it took our guy so long to concur and change it.

He replaced the pump and rebalanced the upstairs rads 2 days ago. He left it running on CCIII.

The pump was near silent running in CCIII and there was no vibration or resonating in the system.

Yesterday we tried CCII and that works perfectly as well.

We have set the TRVs between 2 & 3 and the boiler to 3.5.

All radiators are hot (top to bottom, corner to corner) within 20 minutes.

Boiler is running smoothly and quietly. We can’t remember the system ever running as quietly as it is now.

Once again thank you so much for all your help with this. I have learnt so much from you, which was an invaluable help in arguing the case for it being a faulty pump.
 
That's great to hear.
You could also run it on CPII which gives 95% of CCII flowrate and will save a extra bit of energy when the TRV's start throttling in. Unfortunately, the PP settings which were primarily designed for TRV operation are practically useless on this pump as they are too low except that you have very large flow and return manifolds but I suppose no harm in trying, its only a button push. IMO the DAB Evosta3 is a far better choice ( Ithink, made or owned by Grundfos) as not only has it higher PP settings but also displays the pump head and flow rate.
 

Reply to Grundfos pump making unusual sound/boiler not coming on in the Central Heating Forum area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock