Discuss Grundfos MLE 132E speed control in the Commercial and Industrial Plumbing Forum area at PlumbersForums.net

Messages
13
We have a Grundfos for a domestic water booster application. Everything is set up for constant pressure, discharge pressure sensing and all appears okay, except we cant get the motor to run in "auto". We can run in manual at a constant speed, okay. But we try and go to control, the pump will stop. DI1 is set up as "stop". Now I've tried ground on DI1 as suggested, no change. 5V on DI1, still no change. We have discharge pressure reading, setpoint higher than pressure. Am I missing something simple?
 
Surely there's some software in the controller to stop the pump, ie if it sees no change in pump speed after a few minutes if in auto in constant pressure mode as you don't want the pump running constantly say at night with no demand?.
 
Surely there's some software in the controller to stop the pump, ie if it sees no change in pump speed after a few minutes if in auto in constant pressure mode as you don't want the pump running constantly say at night with no demand?.
Basically, we can not get a 'normal' operating mode selection, only stop, min, max. The start/stop terminals 2+3 (GND and DI1) are connected as per instructions for no external start/stop.
 
Have you set it up via the dongle ?
 
You will require the dongle to set up auto as the front line / bar graph is only for manual
 
We have an MI301M01 IR connection device, but it has no display or any buttons, how does this work?

Yes that’s the device use your phone and the grundfos go app
 
 
Yes that’s the device use your phone and the grundfos go app
Update. We got the ir to work and it controls everything the front display does but like was stated it got the "normal" control mode to work, what happens is the pump normally shows stop, then when you push the start/stop button, the mode changes from stop to normal and you would expect the pump to start however it doesn't, it just sits there in normal mode.
 
So you can see all the settings on your phone etc and make changes / set things ?
 
Front display? That’s yours as that’s the 132e

1661512428170.png
 
I see on the pump you should be able to see a pressure when it’s running correct ?
 
Are these figures on 0 when not running / off ?
 
Discharge / pressure/ flow ?
 
Sounds like maybe the pressure sensor is blocked or broken as when off should rear 0mh / 0 psi
 
Sounds like maybe the pressure sensor is blocked or broken as when off should rear 0mh / 0 psi
Discharge pressure is in discharge line, reading outlet pressure continuously. It is the controlled parameter. This pump will run in manual at a set speed. but when switched to normal it just stops. We are beginning to think there is an issue with the electronics in the controller itself since nothing we can do will make it run in auto (normal) to control, pressure. Unless we are missing something, which is one reason I am here. Several Grundfos techs have looked at it to no avail. My next step is to rip the vfd and control out and put in an ABB580. Will this motor run on a 580? I wonder if there is some priority wiring to look for?
 
Discharge pressure is in discharge line, reading outlet pressure continuously. It is the controlled parameter. This pump will run in manual at a set speed. but when switched to normal it just stops. We are beginning to think there is an issue with the electronics in the controller itself since nothing we can do will make it run in auto (normal) to control, pressure. Unless we are missing something, which is one reason I am here. Several Grundfos techs have looked at it to no avail. My next step is to rip the vfd and control out and put in an ABB580. Will this motor run on a 580? I wonder if there is some priority wiring to look for?
Monday I will try again (since I can now get normal mode) to swap AI1 with AI2 and swap all control parameters to reflect new psi input. Also will try AI1 reading feet as in a tank level control. Change setpoint to a feet level. I‘ll update as time allows. After this if it doesn’t work, out comes the blue blade….
 

Reply to Grundfos MLE 132E speed control in the Commercial and Industrial Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Central Heating Pump - G Pump Force HE-RS25/6PWM-130 Hi, I would be grateful if someone could explain whether our CH system can cope with the AUTO (adaptive mode) setting on this the new pump or which mode it is best set at (recently had our old 3-speed pump replaced with the above smart...
Replies
7
Views
546
Can anyone help, please? I'm looking for a heating system circulation pump for a domestic install, with 3 speeds, where the speed can be toggled electrically as well as via a push switch on the pump body. I'm using this pump with a wood boiler stove, where I want to run the pump at its slowest...
Replies
6
Views
947
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open vented system to sealed / pressurized system, new pump ( UPS3 Grundfos ) all new plastic pipework ( extending ) the 22mm feed and return pipes so no...
Replies
9
Views
992
I'm trying to set up a Honeywell DU145 ABV with an ALPHA 15-60 130 (Model number 59526443) and work out the speed setting. The pump has one variable dial (no C1/2/3 ect). Grundfos support have no info on the pump as its from circa 2001, so unable to help. Its running 5 rads in a small 2 bed...
Replies
17
Views
2K
We live in a 1980s four-bedroom detached house. The time has come for new central heating. The current system is a mild revision of the original heating installed when the house was built, and this revision was largely to replace a life-expired boiler: non-condensing fan flue boiler open...
Replies
13
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock