just nipped up and checked it..... It is 20W on CP1
 
That,s 10.5 LPM @ 3m which is 12.9 LPM @ 4.5m (35W), all adds up.
Even though it doesn't matter now I wonder was the pump just air locked as that problem appeared almost overnight, its a great pity that they don,t have a real vent screw like before.
 
I see that there is an ABV immediately after the pump, presumably because there are. separate zone valves for CH and HW. (A mid-position valve does not normally require an ABV as at least one path is always open.)

However, an ABV is incompatible with PP, CP and Autoadapt modes. You can only use a fixed speed. The correct setting for the ABV will depend on the chosen pump speed.
 
I would agree but I don't know of any true fixed speed, constant curve A rated pumps now ( the DAB Evosta 4-7M did/does appear to have them), if you take the above pump, constant curve 3 gives a constant head of 6M between 0 and 12 LPM (0.7 m3/hr) & constant curve 2, a constant head of 3m between 0 and 10 LPM (0.6 ms/hr), maybe a ABV can be set up, in practice, but how?.
 
I assume that "the above pump" refers to the OP's Alpha 2, not the DAB Evosta.

I would also assume that, if the pump needs to be set on fixed speed III and the flow is less than approx 0.2 l/s, there is something wrong. The most obvious being that the system is not correctly balanced.

However, my reason for pointing out the problem of using an ABV on anything but a fixed speed, is that it will completely mess up the flow through the system. In PP mode the ABV will open more when the flow rate increases, and vice versa; which is the opposite of what is required. In CP mode the ABV will be either permanently open or permanently closed. depending on the setting of the ABV and the chosen CP setting. As for Autoadapt, who knows what will happen!

The setting of an ABV when a modulating boiler is involved is completely different from that when a fixed output boiler is concerned.. With a fixed output boiler the flow rate through the boiler needs to be constant as the boiler output is fixed. So any reduction in flow rate, due to TRVs, MVs etc closing has to be corrected by the ABV opening. If a modulating boiler is used, any reduction in flow rate will result in an increase in flow temperature. So the boiler will modulate down to maintain the set temperature. It isn't until the boiler is running at minimum output that an ABV is necessary.
 
Again, I would agree with you completely but these pumps including the Alpha 2 do not provide true constant curves modes, constant curve ii at 3M has a constant head of 3M between 0 and 10 LPM, it is only when the flow rate exceeds 10 LPM that the head starts falling, in true constant curve fashion, so just as difficult IMO to set up as on constant pressure mode.
If a pump like the Dab Evosta 4-7M (a A rated pump) was installed and set to constant curve 1 at 4.2M then the head will fall to 3M for that required flow of 10 LPM and for example if a modulating gas boiler requires a minimum flow rate of 3 LPM @ 5 kw to maintain a boiler deltaT of 25C then the ABV can be set slightly lower than 3.8M, the ABV will then close once the flow rate increases above 3 LPM as the (dab) pump head will again start falling.
 

Attachments

  • Constant Curve = Constant Pressure.zip
    30.6 KB · Views: 5
Thanks 'Doitmyself' and 'John.g' for your continued comments on this topic -intriguing stuff if not a little beyond me.

I will try to comment as far as i'm able i nthe hope of filling some info gaps

  1. RE ABV: it is after the pump and set at 0.3 (see pic) and there are indeed two separate valves (CH & HW) does that setting seem appropriate?
  2. The BG engineer suggested it go onto setting III and as it ran quietly I thought ok fine. I did hear that setting III was to high for an open system. I'm happy to be guided on this...
  3. By 'messing up flow' I'm guessing that means that the higher system pressure from setting III would 'trick' the system into diverting the heated water as it would if all the TRVs are closed. meaning that the rads wont get the heated water circulation when they are actually open and calling for it.. would that mean that the rads would not get hot? I can tell you that all the rads currently get hot.
  4. RE Modulating boiler V fixed output so mine is an Alpha 18CDR is that modulating? The boiler has a manual dial type thermostat on it 1-9... I have it set at about 6.25

My other thoughts
  1. The sludge on the pump rang a few alarms bells. Its an old system of pipes n rads which I'm guessing is going to be holding some sludge and crud. There is a Fernox filter on it which has been cleaned out twice since weve been here and both times it had an amount of sludge and metallic crud on it tho water from the rads on bleeding runs clear n clean. This tells me at some point we need to consider NEW RADS and a POWER FLUSH. I may well get some quotes at some point. Just don't want to mess with that right now.. I'd prefer to wait until the spring when it ain't so cold and all seems to be functioning at the mo.
  2. I know the pump was fitted within the last 3 years as its date stamped at 3 yrs old... Of course i've no idea how long it had been sat on someone's shelf before fitting. No idea if the ABV setting was considered by the fitter at that point, or even if that's relevant.
hope some this helps with your thoughts on it...

Having considered all this... What pump setting would you recommend? Is there a consensus between you?
 

Attachments

  • IMG_20201127_113709599~2.jpg
    IMG_20201127_113709599~2.jpg
    107.1 KB · Views: 2
I think your boiler does modulate, probably down to 5 or 6 kw but not 100% sure.

I think you were reasonably happy a few months ago with CP1@ 3M and are now running with CP2 @4.5M, I would say either of those, whichever gives you all rads heating equally etc, my system, similar to yours runs at a 3M head equivalent, in PP mode set to 4.3M. Your system should run quite well with a 3M head if its reasonably clean.

ABV setting: I would be very surprised if your heating engineer set the ABV to 0.3 on CC iii (6M) is this would result in a huge recirculation rate of ~ 14/16 LPM, greater than your system demand which would result in a much higher boiler return temp and reducing boiler efficiency, on CP2 setting (4.5M) you would still be recirculating ~ 11 LPM with the ABV set to 0.3, I would say, based on the pump power of 35W on CP2 that the ABV is full of crap and not recirculating anything as I would have expected a power demand of ~ 42W on CP2, IF the ABV is clear and you wish to remain on CP2(4.5M) then suggest setting the ABV to 0.43 which may give you a minimum flow rate of 3 or 4 LPM. If happy to run with CP1 (3M) then set the ABV to 0.28.
If running on CP2 (4.5M) just now then the outlet pipe from the ABV should be roasting at that setting of 0.3 so adjust as required for CP2 or CP1 as appropriate.
Practically, you probably should just set it slightly higher initially and then very very gradually keep reducing the index until you just feel the by pass outlet getting hot, ie on CP2 set to 0.50 and then gradually reduce, on CP! set to 0.35 and do ditto.
 
Last edited:
I've a feeling the ABV hasn't been moved since it was installed and probs never touched when the new (probably more powerful ) pump was installed. It may well be crudded as I cant seem to adjust it. Presumably adjustment is by twisting/turning the plastic cover, but I can't shift it and again don't want to bust it. As there appears to be no way to isolate it cleaning it out doesnt seem an option

From what I remember wasn't Setting II giving me 3M? If I cant adjust the ABV wound it be best to stick to setting II?
 
These were the readings you got early last April and you finally settled on CP1 (3M), see your post #13, page2, but as CC setting ii gives almost the exact same outputs as CP1 for your required flowrates the head does eventually fall off so it might be the more appropriate mode if you do get the ABV cleaned up (or renewed) and operational.

III - 45W (6M)
II - 19W (3M)………….3.0M & 11.6 LPM
I - 6W (1M)
AuotpAdapt went up to 32W but quickly dropped to 12W
PP1 - 10 W (1M)
PP2 - 14 W (3M)……...2.0M & 10.3 LPM
CP1 - 20 W (3M)……..3.0M & 11.7 LPM
CP2 - 35 W (4.5M)....4.5M & 14.67 LPM
 
What is the make of the ABV (if any info)? That would help locate the instructions.

Is the exit pipe (other side from the pump) of the ABV hot all the time, partiularly when the system first comes on?

Grundfos recommend setting the pump to a fixed speed (I, II, III) if an ABV is required.

I would suggest using fixed speed II. This gave a working point of about 0.6 m³/hr and a head of about 3m. The fixed speed curve is almost flat below that point, so the ABV will have to be adjusted carefully to ensure it only opens when the flow rate is below, say, 0.3 m³/hr. The Alpha CDR has temperature senssors for flow and return and will modulate the boiler accordingly to maintain the required flow temperature without exceeding a safe return (recommended differential = 20C).
 
Looks very much like that ABV john.g. but now there's another development. :rolleyes:

The CO alarm went off in the boiler cupboard today. The alarm has an LCD which registered a reading of 46.

Boiler had just restarted by time I got to it, running quietly on setting II at 19W. Obviously I turned it all off opened the windows n Rang BG and they got the emergency Gas guy out who came out quick enough... but it seems it was a one of burst/blow back from somewhere, it was all clear by the time the guy came so its all off until BG can come and check it over again. 🤷‍♂️
 
Thanks. John.g.

I was hoping that there was a locking mechanism on the valve, which there is. The document says:

"Once set, the valve can be locked in position by tightening the screw in the cap."

So all the OP needs to do is locate and loosen the screw, and then he shoud be able to adjust the valve. If it's like most ABVs the adjustment will have a very low gearing, so you will need to turn the adjuster about ten turns to get the pointer to move one division.
 
That should free it up alright but if it was at 0.3 while running in either speed iii (6M) or CP2 (4.5M) then there would or should have been more recirculating than the system demand using a Honeywell DU144 setting chart as a guide, the Biworld only gives a flow rate chart which I don't understand even though I do know what a valve Kvs is.
 
The boiler has a minimum output of 5.4 kW so the flow rate at 20C differential is 5.4/(4.18 x 20) = 0.646 litres/sec. This is shown as the red box on the pump chart below. (The normal working point is the green box.). The head, at the normal point is just below 3m, but it's just over 3m at minimum output.

Pump at boiler minimum.jpg


Now plot the flow and pump pressure at minimum output on the ABV chart as in this pic (I have assumed that 1m =0.1 bar):
ABV at Min output.JPG

This gives a point just below the 0.3 line. Moving twards the Y axis, parallel to the 0.3 line we cross the axis at about 0.29. So the ABV has to be set to 2.9. It's then a case of fine-tuning the ABV so it only opens when required, e.g when both motorized valves close.
 
🤔 Thanks again guys... BG have been ..no fault found after a good check up.... all rads hot and were back onto having a warm house again.... as the ABV is on 3 and setting II runs at 3 i'm gonna leave well alone. Here's hoping 😎
 

Reply to Grundfos Alpha 2 AutoAdapt is slow in the Central Heating Forum area at PlumbersForums.net