We've just moved into a house with the Greenstar condensing boiler. It seems to be struggling a little in that if you're running a bath and someone puts the dishwasher on then it's as if it can't cope. We've come from a combi Boiler and this seems a little ropey in comparison. Maybe I'm expecting too much from this type of boiler? any advice appreciated.
 

Attachments

  • Image 04-02-2020 at 12.56.jpeg
    Image 04-02-2020 at 12.56.jpeg
    21.5 KB · Views: 24
It seems to be struggling a little in that if you're running a bath and someone puts the dishwasher on then it's as if it can't cope.
What exactly do you mean by "can't cope"? Can we assume that the dishwasher is not plumbed into the hot supply? If so, the problem is more likely to be the capacity of your incoming water supply and/or the pipework feeding the boiler and dishwasher.

Anyway, lets start with the simple stuff, is the stop-cock properly open?
 
I think you may be right about the capacity of the incoming water. I've made sure the stopcock is turned fully on. If I'm running several hot water taps then the system seems to struggle with producing enough water. I thought it might be the boiler not able to heat enough to meet demand, but the more I think of it, the water pressure does seem low.
[automerge]1580832532[/automerge]
It’s a regular heat only boiler not a combi to start 😀
Yes, as I said, we moved from a combi to this condensing boiler.
 
I think you may be right about the capacity of the incoming water. I've made sure the stopcock is turned fully on. If I'm running several hot water taps then the system seems to struggle with producing enough water. I thought it might be the boiler not able to heat enough to meet demand, but the more I think of it, the water pressure does seem low.
[automerge]1580832532[/automerge]

Yes, as I said, we moved from a combi to this condensing boiler.
Go to the outside tap and discharge a monitored volume of water over 1 min and see what volume.
Do this at peak time just before school on a weekday, again in the evening peak and about 6am on a Sunday and let us know what you find. Just check the outside tap is on the mains There is a relationship between pressure and volume but you are looking at volume Centralheatking
 
I think you may be right about the capacity of the incoming water. I've made sure the stopcock is turned fully on. If I'm running several hot water taps then the system seems to struggle with producing enough water. I thought it might be the boiler not able to heat enough to meet demand, but the more I think of it, the water pressure does seem low.
[automerge]1580832532[/automerge]

Yes, as I said, we moved from a combi to this condensing boiler.
That’s because you’ve probably got a gravity fed hot water cylinder and not a pressurised system. Have you got tanks in your loft?
 
That’s because you’ve probably got a gravity fed hot water cylinder and not a pressurised system. Have you got tanks in your loft?
No tank in loft, only cylinder on landing.
Cheers.
[automerge]1580841527[/automerge]
Go to the outside tap and discharge a monitored volume of water over 1 min and see what volume.
Do this at peak time just before school on a weekday, again in the evening peak and about 6am on a Sunday and let us know what you find. Just check the outside tap is on the mains There is a relationship between pressure and volume but you are looking at volume Centralheatking
Will do!
 
Hi, I've measured the output and it's averaging at 1 litre per 10 seconds. That's with nothing else being used. Is this low?
 
Hi, I've measured the output and it's averaging at 1 litre per 10 seconds. That's with nothing else being used. Is this low?
6 litres per min is above the statutory min. Your utility have to supply but it won’t be enough to much more than one use around the house at one time. There are totally legal booster pumps but when your neighbours all get one it’s back to square one. You might try installing a new supply from the utility to your house, but if it’s a long way it’s a lot of digging and has to be inspected. Centralheatking
 
Sounds like you may have an unvented cylinder, or a thermal store. You may need someone who is qualified to look at this problem. Pictures would be useful. Thanks.
 
Sounds like you may have an unvented cylinder, or a thermal store. You may need someone who is qualified to look at this problem. Pictures would be useful. Thanks.
Here's a photo of the cylinder.
 

Attachments

  • cylinder.jpg
    cylinder.jpg
    123 KB · Views: 22
See how the cylinder has a small section at the top, that’s a cold water storage cistern, Known in industry as “fortic”. That’ll be your problem, check to see how quickly water is replenished as hot water is Drawn off.
 
See how the cylinder has a small section at the top, that’s a cold water storage cistern, Known in industry as “fortic”. That’ll be your problem, check to see how quickly water is replenished as hot water is Drawn off.
It’s not a combination cylinder it’s a thermal store. The tank is supplying the heating side of the system.

The strainer is probably blocked on the incoming main, where the expansion vessel is. It’s not clear if there’s a PRV on the incoming main on the photo but if there is I’d check that this is operating correctly too.
 
It’s not a combination cylinder it’s a thermal store. The tank is supplying the heating side of the system.

The strainer is probably blocked on the incoming main, where the expansion vessel is. It’s not clear if there’s a PRV on the incoming main on the photo but if there is I’d check that this is operating correctly too.
here are a few more photos. Thank you for all the advice - it's much appreciated.
 

Attachments

  • cylinder 2.jpg
    cylinder 2.jpg
    137.9 KB · Views: 15
  • cylinder 3.jpg
    cylinder 3.jpg
    148.6 KB · Views: 16
  • cylinder4.jpg
    cylinder4.jpg
    177.6 KB · Views: 17
...... Closed ......
 
Status
Not open for further replies.

Reply to Greenstar Condensing Boiler 24 Ri big enough for job? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
131
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
77
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
186
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
218
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock