A bit of advice please. I have a Grant vortex eco 26 oil fired boiler with a riello RDB 2.2 burner on a gravity fed system. If it hasn't been used for a day or two, when it tries to fire up the fan starts and a few seconds later you can hear it attempt to fire, this lasts for a second or 2 and it stops firing but the fan continues. A few seconds later it tries again, lasting a fraction longer but then stops, then a few seconds later it tries again. Each attempt lasts a bit longer and the fan goes continually. After anything up to 15 attempts it seems to be working and condensate starts to appear and slightly warm air comes from the flue, this can take 5 minutes or more. Once it has been running it seems to start straight away when heat called for. Is it normal for Grant boilers to start like this? It is less than a year old and the installers have been back a couple of times, the last time "cleaned a thermo-couple" , but when they have tested it and it has "warmed up" it works correctly until it is left off for a day or 2. They are due back again this week but I have little hope of a fix.
Thank you.
Mat
[automerge]1594651312[/automerge]
Brain fail when writing request, Should have read "cleaned a photocell" sorry about that but it wouldn't let me edit.
 
Last edited:
This is not normal operation.
Is it a digital control box on this burner? White/clear lockout reset button.
Is it a balanced flue?
Are you saying it fires, flame drops and then relights several times before staying in steady state?
 
This is not normal operation.
Is it a digital control box on this burner? White/clear lockout reset button.
Is it a balanced flue?
Are you saying it fires, flame drops and then relights several times before staying in steady state?
Thanks SJB, No idea if it has a digital control box. Boiler just has on/off Temp and Black reset button. Burner has no controls but a dial showing 4. It is balanced flue and NOT a combi. 2 photos attached. It seems to fire, flame then relight but this going by the noises. As I am a homeowner there is no way I will tinker with it myself, that is for the experts. riello.jpgGrant.jpg
 
Thanks for responding.

Going by your words of it fires, goes out, then back on several times, rather than going straight to lockout prompts me to consider a few things.
Unfortunately all of them require someone who knows what they're doing and with the right tools to check.
Perhaps the only thing I can get you to check is if there is anything partially obstructing the flue terminal and creating a micro environment.

The situation you're describing is NOT normal operation. Perhaps you should consider trying a different engineer.
 
Thanks for responding.

Going by your words of it fires, goes out, then back on several times, rather than going straight to lockout prompts me to consider a few things.
Unfortunately all of them require someone who knows what they're doing and with the right tools to check.
Perhaps the only thing I can get you to check is if there is anything partially obstructing the flue terminal and creating a micro environment.

The situation you're describing is NOT normal operation. Perhaps you should consider trying a different engineer.
Nothing causing an obstruction, see photos, as it is still under guarantee I will see what the engineer says later in the week and thank you for the advice.
Mat
flue1.jpgflue2.jpg
 
If its still under warranty then give Grant a call and it won't cost a thing. I suspect its either a box or cell problem, both are common but there are other possibilities.
Please update us on the outcome
 
If its still under warranty then give Grant a call and it won't cost a thing. I suspect its either a box or cell problem, both are common but there are other possibilities.
Please update us on the outcome
hI SJB It has been a long time but part of the problems have been solved, the original engineers eventually called in a colleague who fairly quickly discovered the oil boiler firing problem was down to a poor oil flow due to a partly blocked filter at the oil tank. Once that was cleaned the boiler fires correctly now. As the installation is still under warranty I have been calling the original team back to sort out continual leaks from joints in the 10mm pipework, they fix one leak and another joint down the line starts seeping. They are supposedly coming back to try again for the 7th time soon but I don't hold out much hope so will then resort to a qualified engineer to sort it. No sealant and probably no pipe inserts could have a bearing. I suppose my big lesson is not to automatically trust recommendation sites and to double check with OFTEC registration that the business reference actually applies to this company and not one elsewhere in the country.
 
hI SJB It has been a long time but part of the problems have been solved, the original engineers eventually called in a colleague who fairly quickly discovered the oil boiler firing problem was down to a poor oil flow due to a partly blocked filter at the oil tank. Once that was cleaned the boiler fires correctly now. As the installation is still under warranty I have been calling the original team back to sort out continual leaks from joints in the 10mm pipework, they fix one leak and another joint down the line starts seeping. They are supposedly coming back to try again for the 7th time soon but I don't hold out much hope so will then resort to a qualified engineer to sort it. No sealant and probably no pipe inserts could have a bearing. I suppose my big lesson is not to automatically trust recommendation sites and to double check with OFTEC registration that the business reference actually applies to this company and not one elsewhere in the country.


Hi. I've taken a break from all the sites I frequent on so have only just seen your post. A partially blocked filter will definitely cause the problems you stated. The burner would establish flame and pass control box safety time and then lose flame any time after, preventing it from going to lock out straight away, which in turn would initiate a retry sequence each time.
An oil line should either be flared or compression with inserts. Many people argue flared all the way and many argue compression with inserts, bottom line is either is acceptable if done right and will not cause problems.
I would not necessarily trust recommendation websites, checkatrade etc. A good engineer or firm does not need to utilise these sites as they get plenty of work without, people using sites like that to generate a work income generally aren't as competent as others, although some are an exception.
I hope you find a genuine and good engineer, to be honest the problems you've encountered are basic stuff and its worrying that a firm can not get it right.
 

Reply to Grant Boiler starting up advice in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
174
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
0
Views
107
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
147
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock