Discuss Glow Worm burner cycling on Pmax when trying to gas rate in the Gas Engineers Forum area at PlumbersForums.net

Messages
37
Hi I am gas safe registered, when commissioning glow worm Ultimate 3. Have put into p.01 to gas rate and set at Pmax, but burner keeps cycling on and off rather than running at full rate, so am getting incorrect gas rate, any thoughts?
 
Getting too hot so bad circulation or trvs shut
 
All TRV's are open, im wondering if as its only a small property boiler has got up to temperature and is starting to modulate down, hence giving a low gas rate. Doesnt help when I need the figures to be correct.
 
Run it in hot water mode
 
have tried in hot water mode but they don't have the best water pressure so heats the water up very quickly. Was thinking of sticking it in chimney sweep mode? what do you think
 
The only other way if it’s got a mag filter with valves shut this find a drain off away from the boiler connect this to a hose pipe and drain it off at the same time fill the system to keep it at the correct pressure
 
have tried in hot water mode but they don't have the best water pressure so heats the water up very quickly. Was thinking of sticking it in chimney sweep mode? what do you think
Chimney sweep isn’t max
Sounds like the boiler is oversized?
 

Reply to Glow Worm burner cycling on Pmax when trying to gas rate in the Gas Engineers Forum area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock