hey Guys I wonder if someone could help me out.

I wanted to find out if I could work on this domestic installation. It’s a house with 2 boilers 24 kw each so 48 in total, the gas meter is a g10 which I believe can be used as domestic and commercial. The gas pipe is run in majority 28 mm at 12 meters and 2 metres in 22mm. What would be the volume of gas in as I am aware as a domestic engineer I can work on 70kw and less with upto 35mm pipe and a gas volume of 0.035m3 and less. Appreciate the help thanks
 

Riley

S. Mod
Trusted
Plumber
GSR
Messages
10,622
Reaction score
3,451
First things first are you gas safe?? I’m assuming yes. Daft as it is because it’s pretty specific but we do not discuss has topics in open forum. Send a copy of the front and back of your card to @Riley @Harvest Fields or @ShaunCorbs and get your posts up to ten or more and we’ll get you access to the gas safe only section.
 
OP
I

I-kal

GSR
Messages
17
Reaction score
1
Hi yes I am, when signing up I had to give my gas safe number but I will send over a pic to the above.
 
OP
I

I-kal

GSR
Messages
17
Reaction score
1
Just sent it over let me know is you have received. Cheers mate.
 
OP
I

I-kal

GSR
Messages
17
Reaction score
1
This is the thing it’s over by quiet a bit so I must be doing soemthing wrong. I have been going over books etc to see if my working are correct so I thought someone on here could guide me.
 

ShaunCorbs

S. Mod
Trusted
Plumber
GSR
Messages
22,912
Reaction score
6,057
fill this out

28 mm at 12 meters _________ x 12 =
2 metres in 22mm __________x 2 =

total = ______

+ 10%

total iv _______

g10 meter _____

Ivt _____

its close
 

snowhead

Plumber
Messages
2,786
Reaction score
1,025
Are you adding pipework to the system, in which case it may be under to start but over after the addition?
Or just working on the boilers?
 
OP
I

I-kal

GSR
Messages
17
Reaction score
1
No pipework adding just working on boilers and issuing a landlords gas safety
 

ShaunCorbs

S. Mod
Trusted
Plumber
GSR
Messages
22,912
Reaction score
6,057
so have i

28 mm at 12 meters 0.00054 x 12 = 0.00648
2 metres in 22mm 0.00032 x 2 = 0.00064

total = 0.00712

+ 10%

total iv 0.007832

g10 meter 0.025

Ivt 0.032832
 
OP
I

I-kal

GSR
Messages
17
Reaction score
1
Judging by that it’s very close, will need to make sure measurements of gas pipework is spot on in this case.
 

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers

Plumbase - Plumbing Parts for Plumbers

Underflor Heating Systems by uHeat

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies

Corgi - Plumbing Supplies for Professional Plumbers

Top Bottom