Hello, I'm after a bit of advice.
If you, as a gas engineer, needed to "fault find" on a boiler that has a problem, would you do a flue integrity test as one of the first ports of call.
The boiler ignites, stays lit for 20 seconds or so then shuts off. About 20 seconds later, the boiler re-ignites. This process is repeated throughout the boilers programmed time.
Constant on and off.
Just to provide a bit more background. This problem has persisted since September. It was finally resolved in December on the seventh visit by 3 different engineers.
The problem was a damaged clip inside the flue resulting in CO2 ? being drawn into the combustion chamber.

I would have thought that any reported fault on a gas boiler would start off with a test to measure any CO2 leakage.
I would appreciate someone putting me right about this.
Thanks for your input.
 
Baxi boiler ?
 
Baxi, yes System 36/60
The fault was described by me as "radiators not getting hot and boiler starts then cuts out, then fires up again...etc.etc."
The starting point from the first 2 technicians was "where's the pump?" They couldn't find it and left...
After the first 2 visits I found the pump myself from looking at the main diagram.
Technician number 3 turns up and asks...where's the pump...my reply was polite and to the point..."I think you'll find it inside the boiler"

So, the 3 technicians who came to rectify the fault seemed to think the fault was with the pump. Despite the fact that the problem was obviously within the combustion cycle, it was after all, coming on and going off...constantly.

My question remains, given the extra information, would you have done a Flue test?
 
Not from that description no, but I would probably need to be on site to establish what was happing with the combustion process, and whether it would work under different conditions.
 
So, the 3 technicians who came to rectify the fault seemed to think the fault was with the pump. Despite the fact that the problem was obviously within the combustion cycle, it was after all, coming on and going off...constantly.
In my experience, the symptoms you describe are more commonly due to a failing pump than the type of flue fault that it turned out to be eventually in your case.

The aim of fault finding is to find faults as quickly (i.e. cheaply) as possible. In practice this usually means perform quick and simple tests that detect or rule out common problems first.

If you want certainty, use the manufacturer's 'fixed price repair' service. It'll be more costly on average but will avoid getting stung if something unusual or tricky afflicts your boiler.
 
Hmmm...pump...none of them even knew where it was, let alone thought about trying to locate it. It's inside the boiler for f**** sake. I think I should point out at this stage that none of them were blind.
The first two suggested I should start to rip out various sections of boxing, the second even suggested ripping up flooring in and around the airing cupboard!!
I told technician number 3 where the pump was.
There was nothing wrong with the pump, he left, the fault remained...
 
Hmmm...pump...none of them even knew where it was, let alone thought about trying to locate it. It's inside the boiler for f**** sake. I think I should point out at this stage that none of them were blind.
The first two suggested I should start to rip out various sections of boxing, the second even suggested ripping up flooring in and around the airing cupboard!!
I told technician number 3 where the pump was.
There was nothing wrong with the pump, he left, the fault remained...
You were unlucky and have our sympathy but the problem is now fixed so it's time to move on.
 
Thanks Chuck, I guess you're right.
This still grates though.
We're constantly being reminded about the dangers of CO2 poisoning. Everything is covered by a multitude of ever increasing levels of regulations. We can hardly move without incurring the wrath of some kind of enforcement officer.
Yet, when it does go wrong, the powers that be, seem to be ready to jump to the defense of incompetence.
The boiler was actually shut down and capped off in December "Because it was dangerous"

If it was "dangerous" in December, it was dangerous in September when the fault was first reported.
How many possible diagnoses can there be for "combustion to take place, from cold, and continually shut down in roughly 20 second cycles?" (a supplementary but entirely serious question)

This was the reason our radiators never got hot. There was never any continuous heating going on. Like trying to heat a room by striking one match at a time.
How often does a boiler get tested for the integrity of its ventilation system? (or whatever the dangerous bits are called) Once when commissioned? Once every ten years? Once every service?
I mean, apart from the electrical components or the damn thing actually falling off the wall and crushing you, what else is dangerous except the combustion process.

Ergo, if there is a fault within the combustion process, I don't want to go through it again, light, shut down, light, shut down, light, shut down... Ad infinitum ...how can it be not sensible to test the combustion process...from beginning to end...
I'm genuinely at a loss as to why this didn't happen. But then again, I'm not a gas technician.
It's all witchcraft I tell'ee.
 
If it will only stay lit for 20 seconds it’s not long enough to perform a flue integrity test.
Ah, OK, so the boilers own sensor within the combustion process (forgive the lack of knowledge) was able to detect the CO2 being sucked back into the combustion chamber from the compromised flue (again, I don't know what I'm talking about) and instigate a "shut down"
When it detected that the air was clean, the CO2 had dispersed (again, don't know etc...) it started up again as it was programmed to do?
And so the cycle persists...
How long, as a ball park figure, does the boiler need to be operational for in order for a test to be done? A minute, an hour?
 
10 minutes ideally but 1-2 minutes

The flame was probably being starved of oxygen and would go out
 
If there’s an issue with combustion, then yes, I’d be investigating why.
Thanks, I'm just trying to establish from an independent source, someone with expertise on here perhaps, why it took the best part of 10 weeks for the boiler to be isolated because it was "dangerous". The problem that was present, something within the combustion process, was there from the outset.
That's my take on it, given that the boiler didn't want to stay alight.
That's pretty much the extent of my knowledge, although I'm learning from you guys, thanks.

Perhaps I should ask another question;

My boiler keeps igniting then turning off, sometimes after 20 seconds, sometimes after a few minutes. It then turns on again, and off. What is causing it to do this? What would be the first thing you'd do?

Difficult to answer definitively, I know, without being there, but just some general idea would help.

That is the situation and question that all 3 technicians were confronted with.
Only on visit 6 or 7 by technician number 3 was any part of the combustion process examined, the fault found and a replacement flue ordered.

This is probably going to provoke some mirth and raised eyebrows, but the boiler is covered by one of "those" household policies. (no naming, no shaming)
We made a formal complaint in December, when the problem had finally been resolved. We heard from them on Monday, (not exactly swift in that department either) much ducking and diving. They have offered some £ which is derisory and not really the point.

I think this episode amounts to malpractice, exactly the shoddy treatment that gives the trade a bad name.
I want to try and get all my facts and information as tight as I can, all my ducks in a row, before releasing the hounds. :)

Is that in any way acceptable? 7 visits!
Thanks for your patience!
 
This is probably going to provoke some mirth and raised eyebrows, but the boiler is covered by one of "those" household policies. (no naming, no shaming)
Ahh, the plot thickens. Heard nothing but bad things about these home care cover Scams, whoops, sorry schemes 😉. Once in a while you may get a gem of an engineer, but I’m led to believe they’re underpaid, amongst other things. Hindsight is a wonderful thing, but you’d have been better putting the money into a bank account, not touch it, and use the money for any household/boiler repairs.

As it was said earlier in the thread, most, if not all engineers would be looking towards the pump for an overheat situation, not combustion related, which you said was there from the outset - you only know this yourself because the last engineer diagnosed it.

So, as said, the pump, unless there were other things to consider.

You’ve been let down, and as per @Chuck you have our sympathies, however we’d need to spend a lot of time, and it would need to be out of the public view to give you any specific evidence. You’d be better (if you do wish to persue) getting an independent gas safe registered engineer.

The fact it’s been missed by other engineers shows lack of experience, competence, interest or a combination of those.
 

Reply to Flue Integrity Test. in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
216
  • Sticky
Morning to any Australians lurking around! Register its free, then message me, I'll sort your account out for you. We will need a moderator from each main country too. I'll post this in the Australian forum now.
Replies
0
Views
67
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock