Hi All,

I have a Firebird Enviromax external oil boiler, it has a Riello RDB2.2 C26 burner which keeps locking out.
It has been an ongoing problem, where I've had to call my local guy several times. He gets it going, but it doesn't stay working for long. Its costing me a fortune for his time.

I'm beginning to see a pattern. When it locks out, I remove the side cover, press the reset button and it fires up okay. I can stand there watching it for a good 10 to 15 mins, working fine before I get bored. As soon as I put the cover back in place, it locks out again within about 10 seconds or so.

I wondered whether its restricting the air flow. The vents are not blocked, but I've experimented with just leaving the cover balanced against it, with a good two to three inch gap, it seems to work for a while, but will lock out a while later.

Its peeing down outside, so I don't really want to leave the cover completely off, and expose the electrics to the rain.

Any suggestions of what the issue might be?

I was wondering if the thermostat might be playing up, and that leaving an air gap keeps it cool. But it does seem to be the burner playing up, rather than it being told to go off.

I'd very much appreciate any wisdom or theories, or things to try.
 
In this situation it's usually failed chamber seals leaking products of combustion into boiler casing. With the case on little to no clean air is pulled in and the flame is lost.
 
Unfortunately this is not something you can fix yourself and I will get to why in a minute.
First, you need a new engineer because the problem you're experiencing is quite common and any engineer worth his salt should of considered what I mentioned above on first visit.
I can't be certain for sure it's chamber seals, or flue seals, condense trap failed (if condensing boiler) etc that have failed but that's exactly where I'd start looking and any engineer should have a flue gas analyser and using that would of easily proved if something had failed.
Now, why can't you fix this? Technically you could, beit a door seal, rope seal or a bit of fire cement, however boilers combustion needs to be set with the boiler casing on, which means the engineer setting up the burner needs a flue gas analyser, which you don't have. You could try and fix the initial problem and probably would but you would be unable to leave the burner running in such a state that it burns efficiently, cleanly and safe.
I suggest finding another engineer because it shouldn't take someone multiple visit to rectify a problem which can only be down to a few things. If need be go on the OFTEC website and search for technicians in your area, alternatively say whereabouts you are in the country and one of us few oil engineers on here might be able to help.
 
I have experienced this with an early gerkros condenser fitted with a bentone burner. All seals were intact. Half of the baffles in secondary heat exchanger had been left out, I presume by the manufacturer, as I was the first to open combustion chamber. My reasoning suggested there was too much resistance throughout flue.
 
Hi mundungus
How did your boiler problem get solved? I’ve got exactly the same issue with exactly the same boiler and burner and after 4 visits from the engineer it’s still not fixed! I’ve even explained before his last visit that it’s likely what SJB060685 has very helpfully said what the problem probably was to you, a seal failure! Again I leave the boiler cover off and everything runs fine, I put it on and it’s locked out within minutes!
I’d really appreciate if you let me know how yours got resolved so I can literally spell it out to the engineer!🤦🏻‍♀️ Thanks so much.
 

Reply to Firebird external oil boiler locks out when cover is on. in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
89
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
75
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
226