Firstly I don't install boilers, I'm not a plumber, I commission, service and repair, hopefully anyway. Was called out to a Firebird Enviromax Condensing Boiler after it had sooted up. Boiler is about 3 or 4 years old. Cleaned it out, changed nozzle, checked oil pressure. Still burning black. It's a low level balance flue with a vertical flue kit fitted as it was getting blow back down the flue. What I did notice was the 2 torque screws that screw down tight onto the rubber gasket were lose. The problem is only 1 will tighten and you can actually lift it out. I'm thinking this might be the problem of the sooting up and how do you get around it. What does the actual m6 bolt screw down into or has it rung itself , I'm not sure.
 
Did you take the snorkel off and look inside it for soot. Check the condsate trap is not blocked. You have to run a firebird air rich after a soot up.
 
Easy check to see if you are getting vosiation ( bad spelling) poc in air intake. Put your analyser in the snorkel. Any increase in co will tell you.
What co2 are you running at?
 

Reply to Firebird Condensing Boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi there As you can see from the video below, our pump exploded. The question I have is, this pump is added to a firebird condensing boiler and when we found this mess the boiler and pump were stil operating but the pressure in the boiler was reading 0. Should the pressure switch have kicked in...
Replies
2
Views
403
I have a "Firebird Envirogreen Condensing Combi Oil Boiler 26kW" a part has went and I can't find it anywhere, I was at every plumbers merchant near me but they all need to ring Firebird who are closed till next week. I wonder if anyone can help me find this part please? It's a pressure sensor...
Replies
2
Views
371
Grant Vortex 50/90 condensing oil boiler where the air tube spigot over the fan is not connected to the existing flue, should this be closed off with a Reillo cover plate to stop vermin getting into the open fan motor.If is blanked over will need a further combustion test to confirm adequate...
Replies
1
Views
332
Hi Can you help me determine if my new Navien lcb700 lsx is working as expected? I got the Navien oil boiler installed to replaced an old firebird boiler. The new boiler is a condensing oil boiler and I’m not sure if this is working as expected. I’ve a 300 L water cylinder and after one hour...
Replies
22
Views
2K
Hi. I have a firebird enviromax combi boiler. each time it turns off the motor on the riello burner keeps running for a while then the whole thing goes into lock out. flashing green and red. shouldn't the motor turn off straight away? I'm also getting pressure building up while it's running...
Replies
19
Views
3K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock