J

jack95noon

Moved into an old house that has a vented gravity fed system (cold water tank and feed + expansion tank in the attic). I need to replace all ceased gate valves which is all of them...

The feed pipe from the F+E tank to the oil boiler/radiators has a gate valve in the open position at the moment.

I would have thought this should be in the closed position unless the system needed to be topped up?

Should it be in the closed or the open position? Cant find anything online for this?
 
On the cold feed from the bottom of the cistern. Should be open, and some say shouldn't even be a valve. The water needs to expand up the cold feed when heated and run back down it when it contracts with cooling down after. (If the valve is shut water will use the vent pipe for expansion, but that's not really how it's designed to work).
 
As above, but could and should be IMO a isol valve on the makeup to the F&E tank which I keep shut and open very occasionally to check for system leaks, similar to the top up flexible hose in a sealed system.
 
As above, but could and should be IMO a isol valve on the makeup to the F&E tank which I keep shut and open very occasionally to check for system leaks, similar to the top up flexible hose in a sealed system.
On the mains pressure feed to the ballcock (float operated valve)? Absolutely. Actually, if you are prepared to use it in the way you describe, you need neither an overflow nor a ballcock. (Most people won't bother, however, and a conventional setup will suit them better.)
 
The makeup isolating valve with the conventional ballcocked F&E tank is very useful because if there has been any leakage then its easy to estimate the leakage rate, I am allways a bit surprised that my system never and I mean never takes even a drop of water between the ~ 1 to 2 month check intervals.
 

Reply to F+E tank feed question in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
244
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
143
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
182
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock