I have a Remeha combi boiler and was wondering if anyone on here knows if a boiler can be damaged if the surplus water that it produces comes out of the flue. The flue is in the loft and has brackets to support it to the front of the house, while the boiler is in the back of the house. Should the brackets be positioned so the water runs back into the boiler rather than out of the flue?

I have had several boiler engineers to give advice but some say yes other no...

I don't want the boiler to get damaged.

Any help please? Thanks
 
what model is it ,why is it on brackets to bring it forward if its a condensing boiler it usually goes back into the flue,some flues are on an angle so it comes back into it

it must be gas man as brackets holding it,its a bit unclear i thought she ment boiler held with brackets
 
Last edited by a moderator:
Hello

The boiler is placed in a bedroom at the rear of the house. The flue is vertical from the boiler for a metre or so until it reaches the loft area, then horizontal for several metres along the length of the loft. The flue is supported by 3 or 4 brackets along the length of the loft until it reaches outside. The angle seems to be wrong possibly as excess water drips out onto the front garden intermittently. Should the flue be angled slightly higher to enable all the excess moisture to run back through the boiler?

I hope this is clearer. Thanks!
 
would need to check me corgi book but defo should be on 45,s not horizontal or on a 90 defo certion it shou;dnt be several metres
 
Last edited by a moderator:
didnt understand the last post but the flue should be sloping 3 to4 degrees back to the boiler so that all condensate goes back into the boiler to exit via the condensate drain and not drip out of the flue.max flue length for a 60/100 flue on a 28 combi is 6metres dont forget to deduct 1.4metres for each 90degree elbow though.
 
obviously my question cant be answered without seeing the job etc. but i cant help but wonder why the flue has been taken into the loft etc and not out the wall if in bedroom
 
If its a condensing boiler I would expect the condensate to run back into the condensing module and then into the drain via the condensate trap. It is normally undesirable for condensate to drip outside as it stains brickwork and patios.
 
Yer absolutely; The condensate must drain back to the boiler and through its waste system. So think of the flue as being a waste system for water as well as a passage to safely remove products of combustion. If water is running out of the flue terminal, this is an indication that the flue runs the wrong way and will cause problems. Most flues require 2.5 degree's fall, I think? Thats off the to of my head; check with the manufacturer instructions.
 
but theirs the caveat of a fan on the end so some water will be pushed back to the end of the flue its unavoidable and inevitable
 
would need to check me corgi book but defo should be on 45,s not horizontal or on a 90 defo certion it shou;dnt be several metres
you are mixing up a RS boiler with OF rules, i dont know this boiler so cant comment on the total flue length but ALL RS boilers can be done with 90 bends and horizontal flue runs
 
is that true kirkgas cos doing my acs right now and there sayin 45,s only fitted a 30 cdi last week and that was the same 45,s only no 90,s dont think room sealed has out to do with it ,its the length
 
Last edited by a moderator:
Sounds like a Remeha Avanta, which is a RS with concentric flue.
 
Hello

The boiler is placed in a bedroom at the rear of the house. The flue is vertical from the boiler for a metre or so until it reaches the loft area, then horizontal for several metres along the length of the loft. The flue is supported by 3 or 4 brackets along the length of the loft until it reaches outside. The angle seems to be wrong possibly as excess water drips out onto the front garden intermittently. Should the flue be angled slightly higher to enable all the excess moisture to run back through the boiler?

I hope this is clearer. Thanks!

The config sounds ok...the manufacturers instructions will dictate just how far (distance) the flue length can be. It MUST be supported every 1.8meters. If it is a condensing boiler the flue MUST tilt back to the boiler. If it isn't a condenser it can,very slightly,tilt away to prevent rain ingress.
 
90 bends not allowed on open flued appliances ,they are allowed on fan assisted room sealed appliances, metal dust mate you are getting confused with bend resistances regarding how far you can run a combi flue for example 90 bend 1 meter 45 500mm dependent on mi
 
60/100 flue 5m to 8m depending on boiler model. 80/125 flue 25m to 30m depending on boiler model. subtract 1.4m for each 90degree bend, don't include the boiler flue turret. Subtact .65m for each 45degree bend.
 
oops! didn't think it's an open flue...musta missed that bit
 
is that true kirkgas cos doing my acs right now and there sayin 45,s only fitted a 30 cdi last week and that was the same 45,s only no 90,s dont think room sealed has out to do with it ,its the length

with all due respect if you are doing your ACS just now it is ideal to get this clarified now to sort it out in your head, check the MI of the 30 cdi, i dont know it, but i think you will find you are allowed 90 degree bends on ALL RS fan flued boiler, but the "effective" running length of the boiler needs to take into account reductions in length for each bend fitted, it is EVERYTHING to do with being room sealed as the fan will overcome the resistance of the horizontal runs and bends, when on an open flue it is preferred to have initial 600mm rise before 1st bend, and again it is preferred to not use 90 degree bends, as under some conditions it will pass or fail a spillage test, obviously fan fleud does not have this prob, i use bpec books but im sure most are similar, bpec have 3 modules on flues, it is all in your training notes somewhere
 
with the performa its even more sever 30he 3 meters inc bends 24he 3 meters inc bends this is on 100mm/4inch vertical section not part of the equation after this you have to step up to 125mm
 
cheers kirk gas but think ill stick to the gas engineer i no and the acs centre am using ,no disrespect,havnt read anything on it yet but will do also ive know for years about 45,s and 90,s from working in city plumbing and speaking to tech lines ,get all the stuff on open flues, distances ect just never seen a 90 on a r/s except straight away were it comes out the boiler anfter that 45,s but if am wrong ,sorry to ye if i am
 
Last edited by a moderator:
cheers kirk gas but think ill stick to the gas engineer i no and the acs centre am using ,no disrespect,havnt read anything on it yet but will do also ive know for years about 45,s and 90,s from working in city plumbing and speaking to tech lines ,get all the stuff on open flues, distances ect just never seen a 90 on a r/s except straight away were it comes out the boiler anfter that 45,s but if am wrong ,sorry to ye if i am

no prob, i can keep this post as long as i need to !!!!!!!!!!!!!!!!!!!!!!!!!!!!
seriously have a chat to both the gas guy and the centre, it is easy for ONE of us to get mixed up :) technically there isnt a restriction to the amount of 90 degree bends you can use on a fan flued boiler as long as you take the appropriate "equivalent length" off the total allowed, although 6-8 bends are potential seal leaks at a later date
 
Last edited by a moderator:
cheers kirk gas but think ill stick to the gas engineer i no and the acs centre am using ,no disrespect,havnt read anything on it yet but will do also ive know for years about 45,s and 90,s from working in city plumbing and speaking to tech lines ,get all the stuff on open flues, distances ect just never seen a 90 on a r/s except straight away were it comes out the boiler anfter that 45,s but if am wrong ,sorry to ye if i am

?????????????????????????????????????????????????????????????????????????????????????????????????????????????????????????
your very wrong,9o degree bends on r/s fanned flued appliances are as common as muck
 
ok fir doos maybe am wrong but illl stick to what i no and how av done it ,no direspect but this how av been learnt on both sides of the counter so am staying like it and in 4 yrs of selling the stuff i can honestly say ive never sold a 90 for r/s except on the first bend not tryin to be a smart rse just wat ive done
 
Last edited by a moderator:
ok fir doos maybe am wrong but illl stick to what i no and how av done it ,no direspect but this how av been learnt on both sides of the counter so am staying like it and in 4 yrs of selling the stuff i can honestly say ive never sold a 90 for r/s except on the first bend not tryin to be a smart arse just wat ive done
if you never sold a 90 bend for a fanflued boiler you must have worked in a very quite merchantsi recently put 3 90 and a 45 on one job
 
ok fir doos maybe am wrong but illl stick to what i no and how av done it ,no direspect but this how av been learnt on both sides of the counter so am staying like it and in 4 yrs of selling the stuff i can honestly say ive never sold a 90 for r/s except on the first bend not tryin to be a smart arse just wat ive done
With respect metaldust9, what you think you know is wrong.
Have a look at the Greenstar CDi MI's. They have a very detailed pictorial on flues and multiple 90° bends. This would be similar for most room sealed fan assisted flues.
 
checked today and legally you can fit a 90 but its not good practice as each 90 adds up to a metre and a half so there for 2 90,s take the flue down to 2 metres as you only allowed 3 meters overall so when someone gets 6-8 90,s on a flue from is behond me so 45,s best as doesnt shorten overall length and i wil stick to how am doing it as ive been fine up to now ,till i come on here
 
Last edited by a moderator:
Just no getting through to some people is there? I don't know it all, that is why this forum is so handy to put your point across and receive some feedback, good or bad. If a number of experienced people say your wrong, unless you 100% categorically know you correct chances are you will be wrong. You put it down to experience, knowing you have learnt something and move on to your next question.
The thing with this industry is; due to the constant upgrades in materials, technology, regulations etc. Know one can profess to know it all.
We are all learning every day.
 
checked today and legally you can fit a 90 but its not good practice as each 90 adds up to a metre and a half so there for 2 90,s take the flue down to 2 metres as you only allowed 3 meters overall so when someone gets 6-8 90,s on a flue from is behond me so 45,s best as doesnt shorten overall length then so you lot need to go back for assesment also all have fun cos am doing it as ive been fine up to now ,till i come on here

a couple of things on your post,
you have changed your opinion on whether it is allowed or not, well done you, i have replied a couple of times on this thread and you mentioned 6-8 bends which was my comment, if you read my post i used 6-8 as an example but did say that many wasn't ideal,
was it your gas guy or the college who told you it was allowed but wasn't good practice? whoever it was doesn't have a clue, , you need to wind your neck in a bit when you come on here, take the advice/banter the way it is intended, to help you, you were given (much needed assistance) and when you ask on here again for advice as you (and ALL of us ) do on a regular basis,
on a serious note if you think you have been doing fine up to now you need to get the head into the books and get some seriuos work done to get to a reasonable standard, but hey dont be disheartened you know you are welcome on here anytime to ask for help!!!!!! we are a friendly bunch it treated with a modicum of professional curtesy and respect,
 
Last edited by a moderator:
Please keep posts on topic and refrain from personal remarks,if members come across any personal or provocative remarks ,please report post and do not respond

As mentioned before,it is important to all members present and future to keep these forums a pleasant and friendly place for all to to visit

Thank you
 
Well said Kirk. That must be the teacher coming out in you;)

Always fancied being a teacher.................then they wasted that one when they banned the belt:D:D

Btw how bad is the snow out EK way? Got a job out there Friday and don't know if i should cancel?
 
For the benefit of Metal re a CDi

30CDi.jpg
You will always have the MI's. Learn to read them.



And for the OP

Broag.jpg

I'm sure you can work it out from this.(and it should slope back to the boiler).
 
Status
Not open for further replies.

Reply to Excess boiler water out of flue or back into boiler? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

A number of issues have been raised from a boiler replacement. Boiler not operating and with no pressure. Tile damage Sprawling pipe layout in kitchen (Retrospective view of alternate option when it was found that promise of removing pipes from airing cupboard could not be fulfilled). Battery...
Replies
21
Views
5K
  • Locked
We're hoping to have a loft conversion done soon, in what is currently a three bed mid-terraced house - we are adding a new bedroom in the loft with en-suite shower and toilet. Currently we have a traditional heating system with boiler in the kitchen, fed by gas pipes under the house, hot water...
Replies
17
Views
3K
  • Locked
This summer I am planning on replacing the heating in my in-laws house. I'll bullet point it for easy reference. Current system is an Ideal Mexico 2 OF floor standing boiler located in the kitchen. Gas pipe is 15mm and runs under concrete floor. System is a C plan, pumped, one pipe CH and a...
Replies
14
Views
104
Billy Bob Bob
B
  • Locked
I am fairly certian this would be okay to do but wanted to double check. Without having the manufacturers instructions or ringing tech I would not know but would it be okay to run a vertical flue 4 meters up from an airing cupboard, through the loft and out through the roof. If so what is...
Replies
11
Views
6K
W
  • Locked
Hi I had my Combi Boiler replaced a little over a year ago with an Ariston Micro Genus 32 HE. The previous boiler was the non condensing 27kw version. Now the boiler is working fine probably good for about another 2 weeks being an Ariston :D Obviously this flue produces a lot more vapour clouds...
Replies
5
Views
2K
Walmtech
W
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock