Gonna replace a faulty Triton Safeguard + in my rental property, was gonna change like for like until I noticed the price. Why is a Safeguard + £300 when I can get another, say a Triton T80 10.5 for less than £150?
 
Yes, I would go for the T80 but check out a few items first.

Ensure that the shower you are replacing is a mains supplied shower and not supplied from the cold water storage tank (CWST), if supplied from the CWST it will have its own integral pump and should be replaced with a T90 which is also CWST supplied and also has its own integral pump and will be un affected by any mains pressure changes.

If the shower is mains supplied then the T80 is the replacement but IMO requires 2.5 bar minimum static downstairs to provide 1.5 bar dynamic upstairs if the shower if installed here.

Also, a 10.5kw shower will require 10 M2 cable, the existing shower may have 6 M2 and only suitable for a 9/9.5kw shower.
 
Last edited:
As above Thermostatic control with reliable water temperature delivery, a T80 easi fit will be ok as a replacement just match the kw output of the Triton safe unit 10.5 kw maybe a bit high for your electric supply , 8.5 kw is the norm . Kop
 
Yes, I would go for the T80 but check out a few items first.

Ensure that the shower you are replacing is a mains supplied shower and not supplied from the cold water storage tank (CWST), if supplied from the CWST it will have its own integral pump and should be replaced with a T90 which is also CWST supplied and also has its own integral pump and will be un affected by any mains pressure changes.

If the shower is mains supplied then the T80 is the replacement but IMO requires 2.5 bar minimum static downstairs to provide 1.5 bar dynamic upstairs if the shower if installed here.

Also, a 10.5kw shower will require 10 M2 cable, the existing shower may have 6 M2 and only suitable for a 9/9.5kw shower.
Thanks for the info, shower is downstairs and comes from mains, electrician ran a new cable in last year was a huge thing but I'll check with him. Spec on the 9.5kw shower says 3.9tlts and 1bar min where the 10kw has 1.5bar minimum. What's the chances of a one floor cottage having less than 1.5bar or should I check it beforehand?
 
Thanks for the info, shower is downstairs and comes from mains, electrician ran a new cable in last year was a huge thing but I'll check with him. Spec on the 9.5kw shower says 3.9tlts and 1bar min where the 10kw has 1.5bar minimum. What's the chances of a one floor cottage having less than 1.5bar or should I check it beforehand?

Downstairs is worth 0.5 bar but no harm in checking if you have a pressure gauge, also in the summer, a 10 kw shower will have to flow 5.7 LPM to give a showering temp of 40C from mains at 15C., the thermal cut out (TCO) would operate (48C) at 4.3 LPM from 15C. If the old shower, even broken, can still flow water you could turn it to its coldest setting (temp control) and see what it flows, any 9 or 10 kw shower should flow 8 to 10 LPM on the coldest setting.
 

Reply to Electric shower swap in the USA area at PlumbersForums.net

Similar plumbing topics

    • Like
Hoping someone can please help. I have an intermittent fault with my electric hot water. I have an older style electric hot water service that heats on controlled load over night. The large tank is in roof space of 60s built villa unit. Every few mornings, no hot water will come out of...
Replies
6
Views
406
Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the cause. I would like a flow rate of about 12L/min. Here is my set-up: Standard gas boiler (not a combi) in the kitchen, have cold water tanks in the...
Replies
14
Views
805
Essaboy
E
D
I currently have an 8.5kw electric shower on a gravity fed system in bathroom which doesn't give great flow when hot turned up but to get a 10mm cable to fuse board would be really difficult at best (I've checked and on 6mm at the minute) I would like a mains shower however changing to unvented...
Replies
1
Views
378
I want to swap my electric shower to a power shower. I have a 200 litre pressurised hot water tank in the loft (not a combi boiler) the hot side has a pump and decent flow, but the cold side/hot side has not got an equal pressure as the cold is just mains fed and would say the flow is below...
Replies
6
Views
781
Hi, After years of using a pumped electric shower (Triton t80 pumped), it's now dying and I'd like to replace it with a 'normal' mixer shower running off the vented hot water tank as this is now largely heated by solar PV . When we first moved to the house there was a shower head coming off the...