Hi anyone. I have the F28 code on this unit. Gas IN is fine and on start up fires but within a second or two, the gas valve shuts. Taken the valve apart and the diaphram is ok,no splits.
S code runs thru 1, 2 & 3 but will not progress to 4( burner ignited). Checked the low voltage solenoid and getting 35 V1 & 17.8 V2(53 Ohms across 2 outer pins). Vaillant say in their opinion it is the pcb but having changed it, the problem remains. The fan gives 418-420 rpm reducing to 380, again vaillant say this ok for initial start and within 10% range.
I've also changed the sparker & ioniser and had the burner out,inspected & cleaned. The 2 connections to gas valve give me 21.8v reducing to 15 then zero, now. Could this gas valve in fact be faulty, even tho the solenoid readings say otherwise?
continuity runs thru all connections and earth is good!
Anyone know where to look next, other than blind replacement?
I have a noodle, and it's being Baked!

Thanks for any help.

PS.. only just registered so not allowed at this point to access the gsr private advise forum.
 
Last edited:
Sorry Virgo, it appears you’ll need to wait, you’ve just discussed a lot on an open to public forum, of gas components - site rules. How old is the Vaillant? Any other gas appliances? If you’re desperate, try diynot.com, approval is usually pretty quick.
 
Sorry Virgo, it appears you’ll need to wait, you’ve just discussed a lot on an open to public forum, of gas components - site rules. How old is the Vaillant? Any other gas appliances? If you’re desperate, try diynot.com, approval is usually pretty quick.
ok, i see. thanks for replying. Shame i wasn't informed a bit earlier by someone/anyone. I would have removed it, or moderators could have?. I've just read the reason why i must wait, not sure i get why an engineer can't access the engineers part, without posting a 100 or more posts first!
defeats the object of helping each other.

cheers anyway.
 
ok, i see. thanks for replying. Shame i wasn't informed a bit earlier by someone/anyone. I would have removed it, or moderators could have?. I've just read the reason why i must wait, not sure i get why an engineer can't access the engineers part, without posting a 100 or more posts first!
defeats the object of helping each other.

cheers anyway.
As I said try diynot.com, zero post count for privileges of gas side, plus some vaillant engineers dip in time to time.
 

Reply to Ecotec plus 824..F28. in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
131
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
191
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
186
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock