Air source heat pump, unvented cylinder with underfloor heating.
When calling for hot water the flow pipe gets quite hot but when calling for heating thw temp drops considerably.
Is this normal? Why would this be apart from the cylinder will need to be heated quicker?
 
Depending on the outside air temperature, it could be the weather compensation reducing the flow temperature or it could just be designed with a lower flow temp to increase efficiency.
 
Last edited:
It will be built into the unit and still controlled by room stats. Heat pump has an external sensor in the unit. Controller will have heating curve built into software. Most decent heat pumps have weather compensation as standard.
 
Last edited:
It is normal that the flow when heating the DHW should be considerably hotter than when heating the house.

When there's a call for DHW, the HP fault created by high flow temperatures is usually overridden in the ASHP controller so that it can get the DHW up to 50°C plus.

When DHW is satisfied it should revert to heating. If it's an S plan that the heating system 2 port valve would usually be a NO valve so that as soon as DHW satisified the HP can dissipate its heat via the heating circuit (means that in summer even if no call for heat when DHW satisified you'll get a minute or so of flow to the heating circuit), if it's a Y plan, it will do that automatically.
 
Thanks gor that worcester, that explains why all the ones ive installed seemed to ramp up in hw mode.
This particular one was linked to underfloor and a heated towel rail circuit.
Had a 3 port valve to the hw and underfloor manifold and then a 2 port to the towel rail. Individual polypipe programable room stats to each room apart from the towel rail rooms which must have been linked to another stat somewhere. No towel rails fitted so unable to tell although the 2 port was open so calling for heat but no circuit to flow through.
 
Last edited:
Status
Not open for further replies.

Reply to Ecodan query in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Does anyone know of a weather compensation unit that can be fitted to a cylinder? I have an Ideal Logic Max H24 which heats a thermal store. The boiler can take an Ideal weather compensation unit to raise the target flow temperature as the outside temperature drops, but the store temperature...
Replies
0
Views
352
T
Hi We urgently need to get our h/w cylinder replaced because it's leaking. Our current system is oil boiler feeding underfloor downstairs, radiators upstairs and an unvented hot water cylinder for hot water. We are thinking of moving to a heat pump at some point but aren't ready to do this. My...
Replies
2
Views
354
Hi looking for some advice here if anyone would be so kind. Our existing system consists of an Ideal Logic Heat H15 heat only boiler paired to a 180L Kingspan Tribune XE Unvented Indirect Hot Water Cylinder (this is the Dual Stat version). Zone 1 (Downstairs) consists of 7 Radiators + Plumbed...
Replies
19
Views
2K
Trying to find out exactly what happens when my system boiler is called to supply the radiators and hot water cylinder at the same time. For example today, whilst the boiler was on heating the water, the room stat triggered the boiler to supply the rads. The diverter valve installed in the...
Replies
7
Views
460
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
442
losing pressure
L
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock