Hi all

I have a promax combi 28 he plus, around 10yr old. Been serviced.

E119 error came on. Usually the pressure has dropped.

Pressure is fine. Tried it at 0.5, 1, 2, 2.5. No joy

Tried draining to zero and refilling.

Tried reset the system via dial.

Had new pressure switch, no good. Tried refil / reset a few times.

Expansion vessel is fine.

Officially out of ideas! Any help would be appreciated. Had a magnaclean fitted about 3 month ago by British Gas and new heat exchanger. Other than that, no work on it.

Looked all over internet for ideas, and all bases seemed to be covered, but obviously they are not!

My thought is that the pressure switch must go onto something when screwed in, and wondering if that particular sensor is covered in yukky stuff, ad the switch I took out was!

As above, any help appreciated

Thankyou
David
 
Status
Not open for further replies.

Reply to E119 error - pressure ok, new pressure switch in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hiya fellow gas engineer. Need some help on this boiler fault. Went out to this E133 Error on a Potterton Titanium 24 (GC: 47-393-39) I checked the inlet standing pressure which was at 25mb. Boiler attempts to fire and the pressure drops by 1mb but the gas valve doesn't open. Checked the black...
Replies
9
Views
419
P
Hi All, I have replaced my existing Shaw and Mason chrome set with the Shaw and Mason forward bowl spindles/ Handles. I have kept the same tap or the water dispensing unit. The water pressure has reduced after I made the changes. I installed the original spindle back but same low pressure. If I...
Replies
0
Views
257
PRJSyd
P
Hi everyone, New here & my first post! I have a Worcester greenstar 24i, it is a conventional boiler, it has a water tank upstairs. For the past year the hot water when turned on was intermittent. I repressurised the expansion vessel to 1 bar and the hot water switch when turned on worked...
Replies
26
Views
2K
Hi, We moved into a new property yesterday and are a little baffled by the heating/water tank situation. The previous owners unhelpfully left any kind of instructions/manual and therefore trying to figure out ourselves. We have what looks like a boiler/water tank system (coming from a standard...
Replies
3
Views
292
After researching as much as I can to sort this problem, I keep reading that if your Ideal boiler has an F1 code and the pressure is low, it needs topping up. If it has an F1 code but the pressure is fine, then this indicates a potential pressure sensor fault. What if it was low (completely...
Replies
3
Views
870
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock