I’m curious why gas is regulated to such low pressures when it enters a dwelling.

My gut instinct says this is for safety but then there is an argument smaller pipes could be made from stronger materials, have smaller leak paths and are less likely to be damaged.

Given this seems to cause issues I assume there is a sound reason for this, or is this a legacy from the days of town gas?
 

ShaunCorbs

S. Mod
Trusted
Plumber
GSR
Messages
22,944
Reaction score
6,075
I would say back in the day from towns gas

And tbh don’t think the net will hold much more pressure it’s leaking enough as it is :D
 

Last Plumber

Trusted
Plumber
GSR
Messages
3,787
Reaction score
1,172
I’m curious why gas is regulated to such low pressures when it enters a dwelling.

My gut instinct says this is for safety but then there is an argument smaller pipes could be made from stronger materials, have smaller leak paths and are less likely to be damaged.

Given this seems to cause issues I assume there is a sound reason for this, or is this a legacy from the days of town gas?
The pressure in the network varies. It is brought down to the pressure we require to operate appliances to the manufacturers performance requirements. In other words, it's enough.

It is better to have gas pressure as low as possible for safety reasons e.g. if it leaks at a higher pressure, more will escape. If that occurs near or within residential areas, there is a high risk of damage, injury or even death from fire or explosion.

Underground pipework is old (a lot of it is) and leaks anyway, so if the pressure is higher than required, there will be more repairs to carry out, more complaints and most importantly, more risk of explosion. Those are few of my thoughts! I hope they help?

Towns Gas pressure was lower than the current pressure at the point of entry to a dwelling, (roughly half or there and there about).
 
OP
O

OffshoreGas

Active Member
Messages
364
Reaction score
69
The network seems to run at the sort of pressured you’d kind of expect. It’s when it actually reaches a property and is regulated down to 30mbar it seems a bit odd.

I guess if you put a screw through a pipe it will leak at a lower rate.
 

firemant

Plumber
GSR
Messages
910
Reaction score
273
The network seems to run at the sort of pressured you’d kind of expect. It’s when it actually reaches a property and is regulated down to 30mbar it seems a bit odd.

I guess if you put a screw through a pipe it will leak at a lower rate.
Hmm. Maybe you should stick to the North Sea?

I don't actually know what the pressure is in London mains, but I do know that there is not enough pressure in the network to provide a universally satisfactory 24hr supply to dwellings in dense urban areas.
 
OP
O

OffshoreGas

Active Member
Messages
364
Reaction score
69
Hmm. Maybe you should stick to the North Sea?

I don't actually know what the pressure is in London mains, but I do know that there is not enough pressure in the network to provide a universally satisfactory 24hr supply to dwellings in dense urban areas.
A helpful and informative comment, much appreciated.
 

Pssst

Plumber
GSR
Messages
587
Reaction score
128
The low pressure network can run at a theoretical max pressure of 75mb. Having said that, the highest ive seen is about 50mb standing pressure which many people would be glad of. Typically the standing pressure would be 23-30. As more and more older cast iron mains are replaced with plastic,it will be possible to admit higher pressures to those sections.
 

Reg Man

Trusted
Plumber
GSR
Messages
3,015
Reaction score
1,046
You are talking about medium pressure gas main. Regulator for domestic is set to 20 to 23mbar working pressure. Standing pressure 25mbar. anything outside this perimeter requires attention. Please don't confuse this forum with what you think is clever. The forum is a mainly domestic and light commercial.
 

Gasmk1

GSR
Messages
1,113
Reaction score
318
The pressure in the network varies. It is brought down to the pressure we require to operate appliances to the manufacturers performance requirements. In other words, it's enough.

It is better to have gas pressure as low as possible for safety reasons e.g. if it leaks at a higher pressure, more will escape. If that occurs near or within residential areas, there is a high risk of damage, injury or even death from fire or explosion.

Underground pipework is old (a lot of it is) and leaks anyway, so if the pressure is higher than required, there will be more repairs to carry out, more complaints and most importantly, more risk of explosion. Those are few of my thoughts! I hope they help?

Towns Gas pressure was lower than the current pressure at the point of entry to a dwelling, (roughly half or there and there about).
thats why after midnight the grid pressure is lowered to lower the gas leak rate
 
OP
O

OffshoreGas

Active Member
Messages
364
Reaction score
69
thats why after midnight the grid pressure is lowered to lower the gas leak rate
I’m quite sceptical about that, gas distribution still utilises quite a lot of positive displacement and turbine flow meters, if you change if you changed the pressure by any significant amount these would give massive errors unless you do a lot of maths.
 
OP
O

OffshoreGas

Active Member
Messages
364
Reaction score
69
You are talking about medium pressure gas main. Regulator for domestic is set to 20 to 23mbar working pressure. Standing pressure 25mbar. anything outside this perimeter requires attention. Please don't confuse this forum with what you think is clever. The forum is a mainly domestic and light commercial.
It wasn’t meant to be clever I was just curious why such a lot pressure is used domestically. Kind of seems like it causes problems like having to run 28mm gas pipes to boilers.
 

Gasmk1

GSR
Messages
1,113
Reaction score
318
I’m quite sceptical about that, gas distribution still utilises quite a lot of positive displacement and turbine flow meters, if you change if you changed the pressure by any significant amount these would give massive errors unless you do a lot of maths.
I’m quite sceptical about that, gas distribution still utilises quite a lot of positive displacement and turbine flow meters, if you change if you changed the pressure by any significant amount these would give massive errors unless you do a lot of maths.
 

ShaunCorbs

S. Mod
Trusted
Plumber
GSR
Messages
22,944
Reaction score
6,075
Thought of this thread when I saw this :D

DA61B11D-DB0A-480D-96A1-09237205C4C7.png
 

ShaunCorbs

S. Mod
Trusted
Plumber
GSR
Messages
22,944
Reaction score
6,075
They'll be cooking more than few steaks there ^^^^ then.
Bread maybe?
Grain dryer it was, high pressure set up scented onsite
 

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers - Plumb Advice

Plumbase - Plumbing Parts for Plumbers - Plumbers Advice

Power Shower Booster for Power Showers - Plumbing Advice

Underflor Heating Systems by uHeat - Plumbing Advice

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies - Plumbers Installation Advice

Corgi - Plumbing Supplies for Professional Plumbers - Advice for Plumbers

Top Bottom