Hi Everyone,
thought I'd pick your brains on some ideas I have for controlling a DHW secondary circulation pump circuit that I'll be installing as part of a new build. The DHW supply will consist of an Air-Water Heat Pump source linked to an unvented cylinder (at mains pressure). Never had the need to do secondary recirculation before, but understand the basic control using timer and temperature sensor on the return flowpipe. However, 2 scenarios exist which, as much as I looked, cannot find any posts that point to an efficient solution. I've got ideas, but don't know whether they have hidden (or unthought of) issues, or whether there is a more elegant solution to cover them. So, I am looking for feedback on these:

Scenario 1 - 'The 3am Bathroom Call'. Outside of the timer/pump being on, how to minimize draw off time (and associated wasted water)? I'm thinking to install a simple flow sensor in the outflow of the cylinder which would switch on the pump (assuming temperature in return flow is below limit). My thinking is that it would pull some of the 'cold' water past the outlet tap at the same time that the tap is emptying into the sink and hence reduce the time/water waste before hot water reaches the tap. Not the perfect solution, but with the pump pulling between 1 - 2 l/s there should be a noticeable improvement, shouldn't there?

Scenario 2 - 'The Family Sunday Morning Church Outing'. Simply put, how to control the system when the hot water cylinder is emptied of hot water e.g. multiple baths/showers at the same time. If the water temperature in the cylinder is below the limit, then the return flow temperature will never reach the pump's switch off point. So the system will continually recirculate tepid water. Therefore I'm thinking to add a second cylinder thermostat (or branch off existing?) that would switch off the recirc pump until the desired temp is reached.

Hope my explanations are understandable enough and look forward to your wise words...

Thanks,
Stephen
 
Use a pir in each bathroom to control the src

as for running out of hot water you should size your system for max demand

can’t use plastic pipe on a secondary return circuit so no speedfit or hep or etc
 
Use a pir in each bathroom to control the src

as for running out of hot water you should size your system for max demand

can’t use plastic pipe on a secondary return circuit so no speedfit or hep or etc
Thanks Shaun,
I'd thought about PIRs, but discounted it on costs and complexity - 6 PIRs/wiring vs 1 Hall sensor next to the pump.

Regarding the capacity, it will be sized for max demand, but I can envisage a scenario whereby the tank is almost emptied (think a bath and 2 showers run at the same time). The pump will then be circulating tepid water until the heat pump rebuilds the core temp (I'm told this can take over an hour for a 250l tank). So I'm thinking it better to disengage the pump until the cylinder is back to temp.
 
The hall sensor won’t come on as no one has walked past it ??

Will your water mains cope with around 50lpm draw off ? So min water mains pressure and flow 6 bar and around 50lpm dynamic

also set the system up for priority hot water 400l around 30-40 mins heat up from cold

have you had a word with your plumber / heating engineer as he should be designing a system for your needs ?
 
Do you really need hot water for the occasional 3am bathroom visit?

Time your hot water for a boost during peak use age and you shouldn’t run out.
 
The hall sensor won’t come on as no one has walked past it ??

Will your water mains cope with around 50lpm draw off ? So min water mains pressure and flow 6 bar and around 50lpm dynamic

also set the system up for priority hot water 400l around 30-40 mins heat up from cold

have you had a word with your plumber / heating engineer as he should be designing a system for your needs ?
Shaun,
Hall Effect Flow Sensor :)

Not sure I would have the mains pressure to run them all simultaneously, but it should easily cope with 2 showers. Hence running a bath and then after that 2 showers together would be a distinct possibility in a 5 bed house. Eventually the hot water will run out; I'm just trying to think of a way to having the recirc pump running unneccesarily
 
Have you got one in mind as it would need to be 1”bsp connections

wouldn’t run out if it’s constantly reheating
 
A Hall effect flow meter / sensor ?
 
A Hall effect flow meter / sensor ?
yes - you can pick up a 1" Hall sensor with brass body and stainless steel impeller for about £12
1618173728390.png
 
Needs to be wras approved as it’s on mains water as that’s likely to have lead in it
 
Hi Stephen - I have a 300L Vailant auroSTOR solar cylinder and similar situation to your Scenario 2 I was thinking of installing a flow sensor and a thermostat so that the DHW circulation pump would only run when i) the timed control is in an on phase, ii) the cylinder was at a specified temp and iii) water was being drawn from the cylinder.


Have you implemented a solution are you pleased with it?
Thanks
 

Reply to DHW Secondary Circulation Control Strategy in the USA area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
202
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
117
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
249
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
198
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
123
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock