Search the forum,

Discuss D2 disharge in the Plumbing Jobs | The Job-board area at PlumbersForums.net

gingalig

Gas Engineer
Messages
217
Hi, I appreciate any help here apologies if it's not the right forum.
I want to clarify that a D2 discharge can be into a 32mm polylropolene pipe with a hepvo trap/tundish with push fit. I would like to be able to fit down the outside of a building with a cage at the outlet with an air gap. If I've managed to misinterpret the regs can you put me straight.

Many thanks
 
Nope you have them correct just need to clip well and use pushfit pipe

You can go into the stack aswell
 
I've usually done them in Copper but from my understanding of the regs your D1 has to be copper with the 300mm drop then a mcalpine hepvo trap/tundish with correctly rated polypropylene 32mm pipe discharge acceptable.

Depends on the length for pipe dia
 
Does this make sense to you?

G3 Document.

3.57 The discharge pipe (D2) should be made of:
a. metal; or
b. other material that has been demonstrated to be capable of safely withstanding temperatures of the water discharged and is clearly and permanently marked to identify the product and performance standard (e.g. as specified in the relevant part of BS 7291- 1:2006 Thermostatic pipes and fittings for hot and cold water for domestic purposes and heating installations in buildings. General requirements)


BPF Pipes Group.

The BPF Pipes Group and its members strongly advise that pipes manufactured to BS 7291: 2006 (Parts 1 to 3) are not used for the downstream pipe D2.
 
Does this make sense to you?

G3 Document.

3.57 The discharge pipe (D2) should be made of:
a. metal; or
b. other material that has been demonstrated to be capable of safely withstanding temperatures of the water discharged and is clearly and permanently marked to identify the product and performance standard (e.g. as specified in the relevant part of BS 7291- 1:2006 Thermostatic pipes and fittings for hot and cold water for domestic purposes and heating installations in buildings. General requirements)


BPF Pipes Group.

The BPF Pipes Group and its members strongly advise that pipes manufactured to BS 7291: 2006 (Parts 1 to 3) are not used for the downstream pipe D2.
It does, although there is an article in CIPHE that refers to the british plastic federation suggesting the use of polypropylene pipework secured at 300mm spacing and conforming to B.S EN 1451-1:2000 is suitable downstream of D2 via an approved tundish adaptor and water less trap. On condition that any connected pipework or soil stack is verifiable. My query was, as there is no access to a soil stack, was if it was ok to discharge through the polyethylene pipework providing a cage at termination with a visible air gap, as the pipework would be verifiable. Which following Shaun's comment and some further reading seems ok.
 
It does, although there is an article in CIPHE that refers to the british plastic federation suggesting the use of polypropylene pipework secured at 300mm spacing and conforming to B.S EN 1451-1:2000 is suitable downstream of D2 via an approved tundish adaptor and water less trap. On condition that any connected pipework or soil stack is verifiable. My query was, as there is no access to a soil stack, was if it was ok to discharge through the polyethylene pipework providing a cage at termination with a visible air gap, as the pipework would be verifiable. Which following Shaun's comment and some further reading seems ok.
Yes. I would say so. I get mine off BES but there are others.
Whilst we are on this subject. Can you see anything wrong in running say a 22mm D1 to termination above ground with a cage?
In other words, no tundish. There are situations where a tundish is not visible and would be pointless. There are also situations where the run is too far to get the fall on a D2. What are your thoughts on those situations?
 
I suppose it would depend on the install, my understanding is that a tundish should allow a visible indicator of any potential issues. And at worst you could probably hear if there was a large escape through prv. I was called to a unvented that had been diy,d a while back and you could hear the water running through the tundish as well as the give away of large pool of water on the floor where the d2 was not connected once it was routed behind the cylinder, the expansion had been connected via a t into the hot outlet which wasnt permissible and inlet set had been blanked off. I can see that a d1 direct to outside would do the job and take your point that some pipework is really hard to visibly see, but if remotely possible would always want to see the tundish as any issues could be ignored or not noticed. Saying all that I'm G3 but not massively familiar with unvented and mainly just try and join the dots.
 
I've usually done them in Copper but from my understanding of the regs your D1 has to be copper with the 300mm drop then a mcalpine hepvo trap/tundish with correctly rated polypropylene 32mm pipe discharge acceptable.
Good practice to do the D1 in copper but I don't think I have ever seen anything in Regs to say it must be, just the limitation of its length (Max 600mm) & minimum diameter, otherwise this could effect the through put of water & therefore the kW rating of the Temperature relief valve.
The is no requirement for a 300mm drop on the D1 before the tun-dish. The 300mm minimum is on the D2 after the tun-dish to reduce the risk of discharge water backing up & overflowing.
When using a HepVO trap connected to the tun-dish (BV1/21 kit) it will ensure that there is always the 300mm due to its total length (hep valve will act a non-return anyway).
 
Good practice to do the D1 in copper but I don't think I have ever seen anything in Regs to say it must be, just the limitation of its length (Max 600mm) & minimum diameter, otherwise this could effect the through put of water & therefore the kW rating of the Temperature relief valve.
The is no requirement for a 300mm drop on the D1 before the tun-dish. The 300mm minimum is on the D2 after the tun-dish to reduce the risk of discharge water backing up & overflowing.
When using a HepVO trap connected to the tun-dish (BV1/21 kit) it will ensure that there is always the 300mm due to its total length (hep valve will act a non-return anyway).
Sorry my bad, mixing me d1s and d2s, every days a shcool day, thanks for the input, always better to understand why and how than just join the dots ;-)
 
Just for info - For those that can get their D2 to the discharge point within the 9 metres minus 0.8 for any bends, I have been interested in using Tectite Flexible Metal tube. It only comes in 15 and 22mm hence restricted to the 9 metre run but looks like a useful product for the job.

It takes the required heat, is flexible with its aluminium layer and stays bent, easily routable and comes in straight lengths and coils for jointless runs.

Just a heads up but it looks useful in some installations. Pegler Yorkshire -
 
I don’t believe that is suitable/ acceptable stig
 
May I ask why as as far as I can tell it meets the requirements. Happy to learna nd be corrected though of course.

I believe temp it’s not rated for discharge I think might be worth an email to peg
 
I believe temp it’s not rated for discharge I think might be worth an email to peg

It's rated to 95 degrees stamped on it which is above discharge temperature. Pegler themselves state in a press release it does "handle temperatures of more than 100°C and working pressures up to 16 bar." but that probably doesn't count and what's actually written on the pipe does.

The regs state it must be capable of withstanding the discharge temperature and T&P relief valves discharge below that temperature.
 
It's rated to 95 degrees stamped on it which is above discharge temperature. Pegler themselves state in a press release it does "handle temperatures of more than 100°C and working pressures up to 16 bar." but that probably doesn't count and what's actually written on the pipe does.

The regs state it must be capable of withstanding the discharge temperature and T&P relief valves discharge below that temperature.

That’s decent to know I would still ask peg then you have no reason not to be able to use it
 

Reply to D2 disharge in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

In the photo there is a grey 32mm push fit elbow between the sink trap and down pipe. I want to replace the elbow with a "male" push fit tee attached to an air admittance valve to stop gurgling noises. I can't find a tee fitting that description, can anybody offer a solution as you can see space...
Replies
6
Views
289
I have a CH boiler installation with a nice simple vertical condensate drain, down and out through the wall to a pipe outside. All is as it should be but I'm fitting an upgraded external pipe setup to include insulation. The inner 22mm pipe mates with the 32mm pipe just inside the house. It...
Replies
8
Views
433
Hello - I have installed a garden sump-pump. In the photo you can see that I’ve replaced the Cloakroom-sink bend that previously went to the gulley with a Tee. Water in Sump vent hose now goes past the cloakroom outlet. Predictably the pump causes gurgling as it creates a partial vacuum going...
Replies
7
Views
526
Engineer has installed several boilers for me. All the condensate pipes have been connected externally into soil stack or rain water downpipe. In each case he just drilled a hole in the pipe, and stuck the condensate in the side, smeared glue everywhere. No boss, or branch. Is this allowed, is...
Replies
2
Views
526
[ASIDE: I did wonder if this was the best forum for this but figured as it was a boiler related issue that the gas engineers would be dealing with it as a matter of course. If I'm wrong can someone let me know and I'll shift it to a better place.] I have a condensing boiler installation...
Replies
5
Views
216
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock