Hello all. Thanks in advance for any help you can offer with this.

Recently had an extension put on the side of the house for a new living room with wet UFH. Rest of the house is on rads running from a gas combi boiler.

I have a feeling that the pipe work has been connected to the UFH pump the wrong way around. This would not surprise me as the sub contractor my builder used was not far from useless.

I've attached a pic showing the direction that the water is trying to flow through the system, but it seems odd to me that the pump would be situated where the water exits the system. The pump makes no noise at all, so I assume it's not activating, either that or it's really bloody quiet!

The 'return' is never more than luke warm, but the flow pipe is too hot to touch.

Am I seeing a problem that isn't there, or was this plumber actually more useless than I thought he could be?

All advice appreciated.

image.jpeg
 

scott_d

Plumber
GSR
Messages
4,166
Reaction score
940
Is there a stamp on the valves with F & R or just coloured handles
 
OP
J

Jordan

New Member
Messages
2
Reaction score
0
Hi Scott,

The side with the blue tap has a ‘C’ stamped into the metal, the side with the red tap has a ‘H’ stamped.

I’ve attached a couple additional photos of the actual setup. The white pipe to the left is the hot flow, the white pipe beneath the pump is the cold return.

I think the evidence points toward it being plumbed the wrong way around, but I just need another opinion before I approach the builder.

Thanks again for the help.

5BD89E22-2F53-48CB-AB93-06ADB8D41BFE.jpeg

E2C5A494-A8ED-4379-B232-01179C354FB2.jpeg
 

Karl

Member
Messages
48
Reaction score
6
As said above the flow should be on the right, ive fitted this type before. Now the reason you can’t hear that pump running is because there is a little stat (in the white box on right) which is linked to the pump. The stat is factory set to 40 or 45 degrees C (can’t remember exactly) which can’t be altered. The reason that pump will never run is because the flow and return seem to be the wrong way around so the water temperature obviously won’t click the pump in. Get them back to sort it
Hope this helps
 

Darren Jackson

Plumber
GSR
Messages
902
Reaction score
381
The UFH is piped up in reverse & will never work correctly as intended. You need to get your man back to rectify it.
 

ballvalve

Member
Messages
42
Reaction score
6
Is the two port valve the right way round,not a very good pic looks like it,s pointing down to me.
 
Thread starter Similar threads Forum Replies Date
A Water Underfloor Heating Installations 8

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers - Plumb Advice

Plumbase - Plumbing Parts for Plumbers - Plumbers Advice

Power Shower Booster for Power Showers - Plumbing Advice

Underflor Heating Systems by uHeat - Plumbing Advice

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies - Plumbers Installation Advice

Corgi - Plumbing Supplies for Professional Plumbers - Advice for Plumbers

Do you have a DAB radio for work?

  • Yes

  • No


Results are only viewable after voting.

Latest Plumbing Advice

Top Bottom