19
Could you explain what natural draught r/s means?
Fanned draught r/s?
Natural draught o/f?
Fanned draught o/f?

Ps. Flues are my weak point so any relevant information would be helpful.
 
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
 
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
Thank you for your help! Highly appreciated
[automerge]1591717469[/automerge]
Flue Categories
A, B, C - flueless, open flues, room sealed

1st digit - denotes method of arranging discharge of combustion
1 - with draught diverter
2 - with out draught diverter

2nd digit - denotes flue draught method
1 - natural draught
2 - fan downstream of heat exchanger
3 - fan upstream of heat exchanger
4 - fan downstream of draught diverter

Open-flued Systems
Open-flued systems


Category B

Balanced Compartments

Self-closing and draught proof door
Switch fitted to the door that turns off the appliance if the door is opened
Door shall not open into a bathroom
If over 12.7kW shall not open into bedroom
Keep closed notice on the door
No other ventilation into compartment
4 parts of an open flued appliance

Primary Flue

Part of the appliance
Creates the initial flue pull to clear the products of combustion
Draught Diverter
Diverts any down draught from the burner
Allows dilution of flue products
Breaks any excessive pull on the flue
Usually part of the appliance

Secondary Flue
Horizontal runs must be avoided
Bend minimum 45°
Keep internal where possible
Minimum 600mm vertical rise to the first bend
Cross sectional area of flue must be at least equal to that of the appliance

Terminal
Stop birds nesting or leaves entering the flue
Minimise down draught
Help the flue gases discharge
Terminals are not required for chimneys with a flue size greater than 170mm if no nesting will occur

Vertex Flue
Air supply taken from the roof space
Draught Diverter min height is 300mm above the loft insulation
The flue above the Draught Diverter must run for 600mm before any bend

Room-sealed Flue Systems

Room-sealed Flue Systems

Category C
Balanced (natural draught) flue
Fan-assisted flues
negative pressure within the casing
positive pressure within the casing
Termination options
Vertical room-sealed flue termination

Vertical room-sealed flue termination

all on google but you should have all this in your viper / niceic book
Could you please provide the link to this page?
 
Last edited:
type into google flue types
 

Reply to Could someone please help me with this? in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
276
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
385
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
217
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
150
I am in process of replacing an existing sink with a new stainless steel one. The existing tap is plumbed directly to copper which means that it is earthed. The new tap will use flexible tails and so will not be earth bonded. My initial search for information suggests that there is no legal...
Replies
5
Views
140
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock