hi all
i have a prob with one of my rads I have 11 rads in the house one does not get hot changed the rad for a new one with new fittings still the same prob the pipework looks about 6mm thinking may be blocked with sludge is it worth it to change to maybe 10mm pipe to see if that solves the prob thanks
 
Probably wasn't necessary to change the radiator. Still, what's done is done.

Try running the system with all the other radiators turned off and turn the pump up if you can. Does that force water through the cool rad? If so, it's probably a balancing issue, or you've just cleared an airlock. Try turning the other radiators back on and see what happens.

Are you getting any flow at all into the new radiator? If not, try removing it and opening one valve at a time into a bucket. That will identify a possible blockage.
 

Reply to cool rad in the USA area at PlumbersForums.net

Similar plumbing topics

Sorry I have sort of asked this before, tried professionals but not great 1st experience hence DIY attempt attempt again. 2 completely cold rad's, another one get pretty warm, flow pipe hot, return v.luke warm. (Both rad's I have manually flushed really well) Hot water works fine, boiler return...
Replies
3
Views
630
I have a downstairs rad that has a 23 year old TRV and it's barely heating up. I bled it, and removed the TRV head and it still just gets a bit warm. It seems to be warm over all the rad, not just at the bottom. The rest of the system heats up fine with the other rads getting hot. It's sealed...
Replies
3
Views
390
Hi, I seem to have lost a bleed nipple from one of my rads somehow. It’s a double rad, one side of the rad has a nipple, the other is gone and I need to bleed it to stop the bubbling noise. How can I fix this please? Is it possible to buy a new one and if so how do I know what to ask for...
Replies
1
Views
281
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or garden, run-of-the-mill British housing estate CH setup. Downstairs radiator, 1 of 2 in our living room, went cold one evening mid-November last...
Replies
8
Views
536
Hi all. I noticed this winter my living room rad only get hot in the top half. Radiator is 1600mm(DP SC) double panel single convector. System was flushed just last year. Both flow and return values are fully open and don't stick. Boiler is serviced each year. Baxi combi boiler about 8 ton9...
Replies
1
Views
390
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock