I already posted a question about this to the MyBuilder.com Ask a Tradesman section but I'm unable to post follow-up questions. Someone has kindly replied that the fix made to my system is dangerous and should be replaced and I'd appreciate it if someone here could validate this advice.

I have a Heatrae Sadia Megaflo unvented system. The water pressure in my flat has decreased over the years and so a plumber replaced what I now know to be the Cold Water Combination Valve (including an attached expansion relief valve connected to a tundish and discharge pipe) with this Pressure Reducing Valve. The PRV isn't connected to the tundish/discharge pipe.

The water pressure is now brilliant again however I noticed that when the boiler is heating the hot water (not the central heating), the gauge on the PRV increases a lot. We have turned down the pressure on the PRV but this isn't a proper fix as surely, the pressure shouldn't increase at all? This feels like a sticking plaster rather than a fix.

What's most frustrating is I bet I could have just replaced the Pressure Reducer Cartridge which would have been much cheaper and less hassle!

I have a few questions:
1) Is it appropriate to replace a Cold Water Combination Valve with a Pressure Reducing Valve?
2) Is the behaviour of pressure increasing when the boiler is running to be expected given the replaced part?
3) Do I need to get the PRV taken out and replaced with a new Cold Water Combination Valve (this looks to be the nearest replacement)?
4) Are there any Cold Water Combination Valves that allow someone to vary the maximum pressure? The pressure used to be so good and if this new valve reinstates it, I'd like to be able to turn it down a little.

Thanks for any advice - I appreciate it!
 
You should have your system checked over by a G3 qualified engineer as soon as possible.

As a minimum this is to verify that the required safety devices are in place and are operating correctly
 
Can you post some pictures of the actual installation please. We cannot really comment properly without seeing what you have.
 
Thanks for such quick responses.

Here are some photos of the original part:

IMG_2793.JPG IMG_2794.JPG IMG_2795.JPG

And the replacement:
20190711_073357850_iOS.jpg
 
Yep, that needs changing. Switch it off and don’t use it until it is fixed. I would also probably turn the stop tap off also.
 
Did the person that carried out the Work hold the G3 qualification allowing them to work on systems like this, based on that repair I would say they probably don’t
 
Did the person that carried out the Work hold the G3 qualification allowing them to work on systems like this, based on that repair I would say they probably don’t
The pictures tell me not a chance mate. Looks DIY to me.
 
Note to the OP it is illegal to work on these installs if unqualified. Also you need the correct parts for the correct cylinder. It’s not just a case of getting best match.
 
Thread closed. As above, get a qualified G3 registered unvented engineer out to fix ASAP.
 
Status
Not open for further replies.

Reply to Concerned about fix made to pressure on Heatrae Sadia Megaflo unvented system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
230
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
382
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock