Search the forum,

Discuss Combi boiler modulation for low heat output in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
5
I'm looking to buy a 24kW combi boiler with only 4 radiators rated at 1.7kW each, so I can later expand and add more radiators.

I expect relatively low heat dissipation from the heating circuit.

If I run the boiler from cold, the water heats up to say 40 degrees in the heating circuit and the boiler shuts off. At what point would it turn on and why is modulation important? Couldn't the boiler turn on when the heat in the radiators drops substantially to avoid cycling on and off and work just fine with low modulation?

I will only have 6.8kW from 4 radiators at max power. When they heat up, I expect that would drop considerably, even with 1:10 modulation I would probably have too much power so the boiler would need to switch on and off repeatedly regardless?
 
This is maybe more a conversation you should have with a manufacturer, also look at different combis because the kw rating is the hot water rating, generally the heating output differs. A baxi 624 has 25kw on hot water but 20kw on heating, non condensing output has a minimum of 6.8kw so your boiler won't really go in condensing mode but should modulate just enough to not cycle. Although I'm not an expert on boiler modulation so I could be wrong.
 

Reply to Combi boiler modulation for low heat output in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
255
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
213
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
201