Hi,

Worcester 28i Junior Combi Boiler

The hot water lasts only probably 2 or 3 minutes and then become cold for about 30 seconds then warm/ hot again... thought it's the limescale blocks the secondary heat exchanger.

Now the plate heat exchanger has been replaced but the problem still exist!

Could be the diverter valve scaled too? Or any idea?

Thanks
 
Hi, I’m having the same problem with my boiler, changing heat exchanger didn’t do anything. Did you manage to fix the problem? If so what did you do?
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the temperature to its maximum?
 
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the temperature to its maximum?
Ours is a Vaillant ecomax and it’s 17 years old so I very much expect to purchase a new boiler but we will be moving house so I really don’t want to be spending 4-5k on a new boiler that we won’t use for long. I have just put the hot water temp up to max now. I think that the plumber who replaced the heat exchanger turned it up and it didn’t make much difference.
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the temperature to its maximum?
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the tempOurs is a Vaillant ecomax and it’s 17 years old so I very much expect to purchase a new boiler but we will be moving house so I really don’t want to be spending 4-5k on a new boiler that we won’t use for long. I have just put the hot water temp up to max now. I think that the plumber who replaced the heat exchanger turned it up and it didn’t make much difference.
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the temperature to its maximum?
No, not really!
The engineer came for the third time and turned the hot water temperature control knob from 4 to 6. After it, the boiler seems fine.
Is yours the same boiler, and how old is it? Have you tried to turn the temperature to its maximum?
Ours is a Vaillant ecomax and it’s 17 years old so I very much expect to purchase a new boiler but we will be moving house so I really don’t want to be spending 4-5k on a new boiler that we won’t use for long. I put the hot water temp up to max about 40 mins ago and just tested, it only lasted 3 minutes before dropping, perhaps I need to give it a day on the max setting. We had a plumber replace the thermal mixer in the shower, but that made no difference. Can’t say I was surprised I had touched the HW copper inlet to the shower when the temperature dropped in the shower and could feel that it was cold, so I was fairly certain that wasn’t the problem. So now I’m stumped.
 

Reply to Combi Boiler Intermittent Hot Water in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
82
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
217
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
304
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock