Yes, it is. The other member has the same problem.Just noticed that its your boiler water pressure gauge thats jumping? re post 34 above, you need a tyre pressure gauge to stick on the air end schrader valve on the expansion vessel, you can then reduce the pressure to 2 bar by pressing the pin on the schrader valve to release some air until pressure gauge reads 2/2.2 bar.
Thanks for explaining it. So, it all looks like I have everything installed what it's needed. It's just some balancing that needs to be done now on that mini expansion vessel. I can easily do this myself. I will post a reply with update.