Messages
13
Hi All! I hope you can give me some advise.
I had combi boiler (Viessman vitodens 100-w 30kW) installed about half year ago. Recently I start hearing one single bang when hot water is opened at any of taps around house. It sound like someone in other room will knock a radiator (not relly loud but you can hear it). After investigating a bit I found it's probably coming from heating circut flow as also when that happens I can see brief jump of pressure on a pressure gauge.
So it only happens when any tap is opened regardless heating is on or off. After closing hot water tap and opening again straight after it's not doing it - only after leave it for some time.
Or maybe it is totally normal with those boilers (as I had previously backboiler with open vented system)?
When I called my plumber (which was installing this boiler) he said (without seeing it) that he never had this kind of problem and start coming with all different possible ways to solve it, but I'm not really keen on spending my money to trial each option.
 
Is there a shock arrestor fitted looks like a 3” silver ball on the cold under the boiler on the pipework
 
As Shaun has said a shock arrestor should be installed I put a double check valve before it seems to sort out the issue. Kop
 

Attachments

  • IMG_20211104_144531521_HDR.jpg
    IMG_20211104_144531521_HDR.jpg
    324.1 KB · Views: 28
Eph combi pack 4 wireless receiver bud this one was wired for open therm , as I said fit a double check valve inline and then the shock arrestor that should cure it . 😉👍
 
Unfortunately shock arrestor didn't resolved it. Double check valve and then shock arrestor close to boiler. Have checked charge on shock arrestor and it's around 3.5 bar.
Nothing changed. Any other ideas?
I'm not sure if that is relevant, but this boiler is in the loft. Also I'm leaving next to water tower and guess I have pretty high mains pressure (but never measured it). Maybe should put some pressure reducing valve?
 
I just had a thought. To be fair, that bang is not straight away after opening a hot water tap. You open the tap, water starts flowing and after maybe 3-4 seconds you can hear that bang. So it doesn't look like it is typical water hammer. My feeling is that this bang happens when boiler shuts central heating flow to prioritise hot water. Also that pressure jump on central heating when that happening... You don't think it might be something to do with boilers internal expansion vessel?
 
I'd still protect the Pipework and appliances from incoming high pressure I have experience with a similar estate I work on at night when no water is being used pressures can reach 8 bar and drop to 3-4 bar in the day , the heating switching shouldn't cause banging unless the system is not connected correctly is there a auto bypass valve fitted ?? Maybe a few pictures would help us here . Kop
 
Hi. So there is a photo of instalation and a video of how it looks when it's happening. I have checked mains pressure today and it's only 3 bar during a day.
 

Attachments

  • 20230422_111242.jpg
    20230422_111242.jpg
    571.6 KB · Views: 20
  • 20230422_111631.mp4
    9.2 MB
Pretty much every time. Just when you open hot water it's doing it first time. Then when you close it and open within short time then it's not happening again, untill you close it long enough for boiler to rest completly (something around 5-10 minutes) then it happens again after opening hot water. I hope you can understand what I mean 😜 Regardless if central heating running or not.
 
This explains it better than I can hope it helps 👍
 

Attachments

  • Screenshot_20230423-075646.png
    Screenshot_20230423-075646.png
    372.4 KB · Views: 16
  • Screenshot_20230423-075455.png
    Screenshot_20230423-075455.png
    155.6 KB · Views: 12
  • Screenshot_20230423-075738.png
    Screenshot_20230423-075738.png
    93.7 KB · Views: 10
  • Screenshot_20230423-075723.png
    Screenshot_20230423-075723.png
    140.1 KB · Views: 10
  • Screenshot_20230423-075705.png
    Screenshot_20230423-075705.png
    131.5 KB · Views: 14
Hello, I am newbie in this forum. I had exactly the same boiler installed around November 2022. It was all fine for some time but then exactly the same issue started happening. I had the little shock arrestor added but that did not helped. I had Viessman checked the boiler and they said that basically everything is fine. They also replaced the little gauge.

I am really curious whether you managed to solve the problem? It clearly something is to do with the pressure and this only happens when I open any hot water tap. Similarly to yours I had open vented system converted to sealed one. I have also installed Aladdin auto vent valves to all radiators.

I also noticed that the pressure reading on the gauge is always higher by about 0.3 bar than on the electronic display but that might be just red herring due to where the electronic gauge actually measures the pressure.
 

Attachments

  • IMG_0468.mov
    8.3 MB
Hello, I am newbie in this forum. I had exactly the same boiler installed around November 2022. It was all fine for some time but then exactly the same issue started happening. I had the little shock arrestor added but that did not helped. I had Viessman checked the boiler and they said that basically everything is fine. They also replaced the little gauge.

I am really curious whether you managed to solve the problem? It clearly something is to do with the pressure and this only happens when I open any hot water tap. Similarly to yours I had open vented system converted to sealed one. I have also installed Aladdin auto vent valves to all radiators.

I also noticed that the pressure reading on the gauge is always higher by about 0.3 bar than on the electronic display but that might be just red herring due to where the electronic gauge actually measures the pressure.
I did some testing in my house to see whether the problem is caused by a high mains pressure which it's a case at my property.

I closed quite a lot the main stopcock valve to reduce the flow of water (I had it fully opened). I made sure that the boiler is on for the central heating. I then flushed the water in the toilet so that I would have a running water for some time. While the cistern was filling up I would then quickly open the hot water tap in the kitchen. Surprisingly no bang when the boiler would switch from central heating to hot water. So as @king of pipes suggested I will also be installing PRV valve. Any suggestions which one would be a good one? I especially want to make sure that once the flow of water is stopped there is no pressure creeping up little by little. How would you also determine if you perhaps need 2 in series (cavitation)?
 
I have installed PRV just after water meter to cover whole house installation and nothing changed. Still the same problem. I even reduced pressure to 2 bar. I think it must be something with boiler itself, maybe diverter valve because it's only when it redirect heating from centrall heating to hot water. Also I have noticed that it's not happening when centrall heating is off for long time.
@andrew77 - from video I guess you don't have your boiler in the loft? As I was also considering if that is creating a problem.
I think I will be contacting Viessmann aswell.
 
I have installed PRV just after water meter to cover whole house installation and nothing changed. Still the same problem. I even reduced pressure to 2 bar. I think it must be something with boiler itself, maybe diverter valve because it's only when it redirect heating from centrall heating to hot water. Also I have noticed that it's not happening when centrall heating is off for long time.
@andrew77 - from video I guess you don't have your boiler in the loft? As I was also considering if that is creating a problem.
I think I will be contacting Viessmann aswell.
That's interesting that it did not fix the problem. My boiler is installed in the kitchen on the ground floor. I live in a 2 storey house (ground floor + first floor) so the pump would be pushing centra heating water up. I also noticed that this is not happening after central heating is off for some time.

I have been also wondering whether it's the diverter valve and I wonder whether because of the high pressure it would effectively get damaged. I am not sure what it's the design of it but there might be a spring inside it that no longer has enough tension to keep it in place.

What I also noticed is that when a central heating goes on there is a kind of hammering noise at the very beginning. I don't know how to describe it so I attached it. The same noise happens when the centra heating goes off. You can hear the noise at about 5 seconds into the recording.
 

Attachments

  • startingnoise.mp3
    245.3 KB
I have the same sound comming from it, but so far I have only noticed it when I run hot water then close it. Boiler then keeps running itself for a minute or so and just before it completly rest - then that sound appear.
 
I have the same sound comming from it, but so far I have only noticed it when I run hot water then close it. Boiler then keeps running itself for a minute or so and just before it completly rest - then that sound appear.
Have you spoken to Viessmann about your problem? When I had first visit from Viessmann engineer as a warranty call he did some checks on the boiler etc. He basically said that everything is fine but that he would recommend change of the diverter valve motor if I remember it correctly. At least this is what he said he would put in his report. However, the second visit from Viessmann by another engineer was that he only changed the gauge. So know I am wondering whether there is something to do with that diverter motor or valve itself but Viessmann is kind of ignoring it.

I am going to go ahead with installing the PRV valve anyway as I think it would still benefit my whole installation anyway as the mains pressure in my house is absolutely ridiculously strong. I am planning on doing it after the King's coronation bank holiday. I will certainly post an update of how it went.
 
No, I have not contacted with Viessmann yet, as I wanted to cover everything regerding installation first (arrestor and PRV). Now I can see the problem still there I will contact them. We will see how it go. I will surely mention to them that there is more of those cases with those boilers so they cannot say it's all fine with it. I will surely update here if I get anywhere with it.
 
Have you spoken to Viessmann about your problem? When I had first visit from Viessmann engineer as a warranty call he did some checks on the boiler etc. He basically said that everything is fine but that he would recommend change of the diverter valve motor if I remember it correctly. At least this is what he said he would put in his report. However, the second visit from Viessmann by another engineer was that he only changed the gauge. So know I am wondering whether there is something to do with that diverter motor or valve itself but Viessmann is kind of ignoring it.

I am going to go ahead with installing the PRV valve anyway as I think it would still benefit my whole installation anyway as the mains pressure in my house is absolutely ridiculously strong. I am planning on doing it after the King's coronation bank holiday. I will certainly post an update of how it went.
Diverted valve is on sealed heating system and shouldn't be affected by mains pressure
 
Diverted valve is on sealed heating system and shouldn't be affected by mains pressure
Thanks for explaining that. That gives me some piece of mind that at least this is not what might be causing it. I am having GAS engineer coming tomorrow to investigate. I measured mains water pressure in my home and at midday it was around 4.5 bar so that it's definitely something to address.
 
Its almost mandatory now to install a expansion vessel on the mains at the combi boiler as some PHE were failing, especially on combis with preheat due to the expansion having no where to go with a closed HW tap.

Not sure, but KOP will know if some/all shock arrestors just have a spring instead of air to take the shock?.
 
So I had the Pressure Reducing Valve installed (i have it set at 2.5 bar max). I also have the mini expansion vessel on the cold feed. Unfortunately the problem is still there.

All the people I spoke to they seem to be lost at trying to identify what the problem might be. I am planning to contact Viessmann again. They need to figure it out especially that I am not the only having that problem.

I started wondering if this is could be caused by hard water (I live in London in an area with hard water), but it's guessing again.
 
Can't say I agree with installing a DCV as a E.vessel/shock arrestor should allow water to move both ways. I would remove the DCV and also set the air end pressure to 2.0 bar
 
Can't say I agree with installing a DCV as a E.vessel/shock arrestor should allow water to move both ways. I would remove the DCV and also set the air end pressure to 2.0 bar
By DCV you mean directional control valve (double check valve)? If yes, then I don't have it installed at all. I think it's the other person on this thread who has it installed. Also, by setting the air end pressure to 2.0 bar you mean setting it on that little expansion vessel?
 
Yes, on the expansion vessel.
Thanks. I just had a look. That expansion vessel is precharged to 4 bars so if I am guessing correctly if the water needs to expand it needs to do it against the membrane that is pressurised to 4bars and this is effectively hard to do. When pressurised to 2bar it will be basically easier for the water to push that inside membrane. I hope my understanding is correct.

And to set the pressurise of the expansion vessel to 2 bar, the procedure I am guessing would be as follow:

1. Close the stopcock valve.
2. Open the cold water tap to empty the water so that there is also no water in the pipe that the expansion vessel is installed on.
3. Use a tool (I don't know the proper name but I am guessing it's some kind of pump with a manometer) that can measure the pressure and effectively release some air from that expansion vessel until the gauge on the tool will show 2 bars.
 
Hello, I am newbie in this forum. I had exactly the same boiler installed around November 2022. It was all fine for some time but then exactly the same issue started happening. I had the little shock arrestor added but that did not helped. I had Viessman checked the boiler and they said that basically everything is fine. They also replaced the little gauge.

I am really curious whether you managed to solve the problem? It clearly something is to do with the pressure and this only happens when I open any hot water tap. Similarly to yours I had open vented system converted to sealed one. I have also installed Aladdin auto vent valves to all radiators.

I also noticed that the pressure reading on the gauge is always higher by about 0.3 bar than on the electronic display but that might be just red herring due to where the electronic gauge actually measures the pressure.
Just noticed that its your boiler water pressure gauge thats jumping? re post 34 above, you need a tyre pressure gauge to stick on the air end schrader valve on the expansion vessel, you can then reduce the pressure to 2 bar by pressing the pin on the schrader valve to release some air until pressure gauge reads 2/2.2 bar.
 

Reply to Combi boiler - bang when hot water opened in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
230
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...