Morning people, I’m in the middle of a listed building refurb. The customer is having overlay ufh throughout and using the original cast iron rads as the supplementary heat. I’m removing the top and bottom entry bushes to have them at the bottom, there’s lots of dried magnetite coming out. I’m thinking of hooking up a powerflush machine whilst we’re at building stage to clean them. I’ve put some of the big lumps into an acid/ water mix and it’s not limescale . What chemicals would give satisfactory results on cold water powerflush?

Thanks

8DFDF3B6-F745-4563-BF47-795BC026FE7E.jpeg


6C7F963A-7498-4A2B-9764-6AC3F84B24BD.jpeg
 
It probably best to keep doing what you are doing.
Remove the entry bushes, belt the heater around a bit and then tip out the dried magnetite.
I would be hesitant putting too strong a chemical through the rads, due to the old paper gaskets used between each section.
It may just be worth flushing with water after getting as much magnetite out while the rad is dry
 
use a rubber mallet and a powerfull magnet as well as
some of the right type of sentinal, or other chemicals.
Ring up their technical number
they will give you good advice. X800 Sentinal but keep it going round loads of times or soak if you can find big enough old tank.
We used to bung them in the pine strippers vat years ago
centralheatking
 
use a rubber mallet and a powerfull magnet as well as
some of the right type of sentinal, or other chemicals.
Ring up their technical number
they will give you good advice. X800 Sentinal but keep it going round loads of times or soak if you can find big enough old tank.
We used to bung them in the pine strippers vat years ago
centralheatking

Just remember, whatever you use, make sure the PH is properly back to neutral when you've done. I suspect it will take as long to do that as clean 'em.
 
Just remember, whatever you use, make sure the PH is properly back to neutral when you've done. I suspect it will take as long to do that as clean 'em.
great advice...forgot that ..and if they are not going to be used for a while, do not store them dry, introduce some chainsaw oil insude and roll it around, then clear it out before use.
chking...good luck sounds a great project
 
Flush them with mains water before fitting
 
I personally would not do it on site after having problems in the past , they should be removed to be aqua blasted stripped down cleaned then rebuilt with new joints , pressure tested then painted before refitting , you are setting yourself up for a failure here make sure you have it in writing that you will not be held responsible for any future leaks on the radiators at the very least . Kop
 

Reply to Cleaning 100 year old cast iron rads. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Have 16 cast iron rads in an old cottage and have been suffering for several years with brass TRVs I bought from a period house store. They look great but have been totally unreliable and around 6-8 have either failed or leaked or both. I'm looking for something to replace them that matches the...
Replies
9
Views
3K
Evening all My rads are quite old (30 yearsish) they are the standard single panel rads. The ones downstairs have large cold patches at the bottom when the heating is on. I want to keep them as I do not want anything deeper to block vital space and because I do not want to change the pipe...
Replies
16
Views
3K
  • Locked
Hi, A customer wants cast iron style rads throughout, 9 or 10 in total but currently has 10mm pipe . Is there any problems installing this type of rad on mircobore? I'm worried about the water content being much higher and it not circulating? Anyone else installed these on mircobore? Cheers
Replies
48
Views
8K
M
  • Locked
Hi all, We'd like to take the plunge and replace our old rads with some 'reclaimed' ones from what used to be Coventry Demolition. However, I'm a bit unsure about how these chunky rads would fit with our existing pipework and I thought I'd ask here before deciding whether to place an order...
Replies
7
Views
995
mattpaints
M
  • Locked
Been installing four reclaimed cast-iron radiators for a customer. To say they've been a nightmare is a bit of an understatement. Couldn't shift any of the old configurations pipework and caps so I have been forced to drill and tap them so that I can set them up with the flow and return...
Replies
17
Views
84
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock