Below my Boiler I have a Pressure Relief Valve which vents to the outside and a drain cock (see image)
The drain-cock is dripping and requires a new washer
If I release this drain cock
Will it just drain down until the Expansion Tank pressure drops to 0bar until no more water flows
Or
Will it drain down the entire CH system ( my worst nightmare)
 

Attachments

  • IMG_20201018_101036922.jpg
    IMG_20201018_101036922.jpg
    1.1 MB · Views: 16
It will drain the entire heating primary system
 
Drain the pressure to zero. Put bucket under drain cock. Close boiler isolation valves.

Whip out the spindle and washer. Quickly refit.

For a bit more time, get a second pair of hands to put the fingers over the drain cock outlets while to attach the new washer.
 
I have been succesfull. I have no isolation valves on the boiler
I closed both valves eitherside of the pump and released the drain cock
Water drained until ZeroBar and then stopped - Pipe dry
Changed tap with no problem,

Thanks for your advice
 

Reply to CH Boiler Drain cock in the USA area at PlumbersForums.net

Similar plumbing topics

Hi I have a baxi duotec combi boiler that every day or other day needs topping up as pressure drops below 0.5bar. When fired up it can reach OVER 2.5bar also whilst running CH. Is this more than likely a flat Expansion Vessel that needs inflating or could there be other possible causes if...
Replies
2
Views
346
Hi all, grateful for your expertise on the following. DIYer, not pro. Rural property in France Single storey. Septic tank. Late 80s construction with concrete slab subfloor. All of the waste pipes run in the concrete, and exit the property at the chamber as pictured, just outside the building...
Replies
1
Views
175
Hi All This is following on from thread I made a few days ago but can't seem to find I'm in a bit of a bind with my CH design where I want to sort all of my rads and do some other bits including fitting a filter but I'm stumped on how to drain down due to how the system is put together...
Replies
0
Views
402
Hi guys. A couple of things. 1 am I better fabricating bends in 14 mm copper for my ch or are 90 degree elbows fine, ref flow, friction ect. 2 my ch boiler, non condensing is playing up, I can get hot water, but when heating is on pipes only get hot for 1st mtre or so? I can hear feel the...
Replies
0
Views
272
Hi All, I have a leaking drain valve off the CW inlet on a Range Cylinder. Am I right in thinking I have to empty the Cylinder below the CW inlet to change the valve? To isolate cold water to the tank to prevent refill, should I just lock off the 1 stop CW inlet or all 3 red stops? Turn mains...
Replies
7
Views
829
newbie184
N
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock